Use velocity pressures in you calculation. It probably won't be enough to fix your problem but it might help. Ryan Peterson Wayne Automatic Fire Spinklers
----- Original Message ----- From: [EMAIL PROTECTED] <[EMAIL PROTECTED]> To: [email protected] <[email protected]> Sent: Tue Feb 19 10:24:57 2008 Subject: RE: Delta Flows That is not enough information to help you. I assume you have a tree. Can you better balance the spacings? Are you over discharging due to minimum pressures? Sometimes smaller piping is better than larger piping to cut down on over discharge. -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris Sent: Tuesday, February 19, 2008 8:04 AM To: [email protected] Subject: Delta Flows I am working on a job and the calc's are kicking my butt! My most demanding head has a delta flow of "0", which makes sense, but allot of the other heads in the remote area are overflowing by up to 10! The calc of course doesn't work, it's 40 pounds over, I've tried everything I know. Any help would be appreciated. Regards, <http://www.firstdefensefire.com/> __________ NOD32 2886 (20080219) Information __________ This message was checked by NOD32 antivirus system. http://www.eset.com _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)