It is a tree, I finally got it figured out. Turns out that the delta head
didn't need to even be in the calc, now everything is fine.


Brian Harris
FDFP INC.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Travis Mack,
SET
Sent: Tuesday, February 19, 2008 10:25 AM
To: [email protected]
Subject: RE: Delta Flows

That is not enough information to help you.  I assume you have a tree.  Can
you better balance the spacings?  Are you over discharging due to minimum
pressures?

Sometimes smaller piping is better than larger piping to cut down on over
discharge. 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris
Sent: Tuesday, February 19, 2008 8:04 AM
To: [email protected]
Subject: Delta Flows

I am working on a job and the calc's are kicking my butt! My most demanding
head has a delta flow of "0", which makes sense, but allot of the other
heads in the remote area are overflowing by up to 10! The calc of course
doesn't work, it's 40 pounds over, I've tried everything I know. Any help
would be appreciated.
 

Regards,

 
<http://www.firstdefensefire.com/>  

 

 



__________ NOD32 2886 (20080219) Information __________

This message was checked by NOD32 antivirus system.
http://www.eset.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to