We always do this even if it means that the first inspection is before a year or a little after a year. Even when properly sloped and drained after a trip there will be build up of water later.
Rod DiBona Vice President Rapid Fire Protection [EMAIL PROTECTED] 605-348-2342 ph 605-391-3553 cell -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Michael O'Brian Sent: Saturday, February 16, 2008 3:43 PM To: SprinklerFORUM Subject: Dry Sprinkler Tests Here in the Midwest it has been pretty cold. This week we looked into two system freezups. Both sites stated they did their dry-pipe trip test and NFPA 25 yearly testing last week. We have always encouraged the dry test to occur during the warmer months and avoid November-March Does anyone else do the same. I think both of these freeze ups would have not occurred if the testing took place in the summer? Michael O'Brian Code Savvy Consultants www.codesavvyconsultants.com _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)