Tyco says 12" for -20'F, 18" for -40'F and 24" for -60'F, the only part that is unclear is if that is total length or the length above the cooler/freezer. We typically just order all 24". We rarely see -60 freezers.

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- From: <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Tuesday, February 19, 2008 3:35 PM
Subject: RE: dry pendant in cooler


What is the length of the dry pendant?  Isn't typical mfgr.
recommendation like 12" minimum?


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Tuesday, February 19, 2008 4:53 PM
To: [email protected]
Subject: Re: dry pendant in cooler

We've found that even when using the DSB-1 (Rubber Boot) for our dry
sprinkler heads we need to foam around the heads in freezers and coolers
to prevent condensation. The first time someone walks on the
cooler/freezer roof/ceiling it can break the seal and allow condensation
on the head.

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message -----
From: "Chris Payne" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Tuesday, February 19, 2008 1:34 PM
Subject: Re: dry pendant in cooler


I have had this happen before and it was due to sealing the head
penetration. We drilled a 2" min. hole and sealed around the head with
spray foam. That solved the problem.

Chris Payne
FPS

----- Original Message ----- From: "GAYLE KNOWLES" <[EMAIL PROTECTED]>
To: "sprinklerforum" <[email protected]>
Sent: Tuesday, February 19, 2008 2:29 PM
Subject: dry pendant in cooler



We have a situation with a dry pendant located minimum 24" away from
coil
in a cooler.  Apparantly, condensation is building up on head and
dripping
water on cooler floor.  This is a cooler box at a Walgreens. Box is
very
narrow and really no other place to put head.  Has anyone experienced
this
before and come up with an idea to correct this problem?  Walgreen's
is
telling us to put a baffle between head and coil.  Not a good idea,
altho,
box is small enough that head will flood entire area, but baffle adds
an
obstruction.  Thanks for any ideas or help.  I actually told them,
coil
was running too cool.  Go figure...I am not a refrigeration person.

Gayle Knowles, SET
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


--
No virus found in this incoming message.
Checked by AVG Free Edition.
Version: 7.5.516 / Virus Database: 269.20.8/1287 - Release Date:
2/19/2008
10:55 AM


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to