Tom and others:
 
I REALLY shouldn't have taken this long to find this, but I'm putting
together new slides for various upcoming presentations on NFPA 14 and
came across this annex material that I had completely forgotten about
and overlooked last week:
 
"A5.4  The committee's intent is to permit the omission of a fire pump
as part of the standpipe system in non-high-rise buildings when the
automatic sprinkler system can be designed and installed with the
available water supply and the flow and pressure demands of the
standpipe system can be provided by the fire department apparatus
through the fire department connection."
 
Obviously this isn't a strict example of the situation you described,
but it underscores what we talked about back in 2003 cycle, and I
believe it further explains the committee's intent regarding combination
manual standpipes and automatic sprinklers.   As does 5.4.1.3 regarding
the use of existing standpipes to supply retrofit fire sprinkler
systems.   The bottom line is that the automatic water supply doesn't
have to be sized for the standpipe system if it meets the provisions for
a manual/wet and satisfies the sprinklers, whether or not that water
supply is a pump or waterworks connection.
 
Steve Leyton
PROTECTION DESIGN & CONSULTING
 
The foregoing is my opinion only and is not intended to represent the
Technical Committee on Standpipe Systems, nor serve as an interpretation
of NFPA 14.
 
 