I can't seem to find it. However my understanding was that the reason for the exception was the expectation of the insulation falling on top of the upright head in this interstitial space and making this head nothing but a thief from the heads above. Following that logic it seems that this would only apply if the insulation was expected to fall quickly in a fire situation. ie: friction or plastic holding it up. I do not see this in the book but I just keep trying to convince myself that this was the case.
Rod DiBona Vice President Rapid Fire Protection [EMAIL PROTECTED] 605-348-2342 ph 605-391-3553 cell -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams - FPDC Sent: Wednesday, March 12, 2008 3:05 PM To: [email protected] Subject: insulation and concealed space NFPA 13 (2002) section 8.14.1.2.13 states that sprinklers may be omitted from a concealed space if the ceiling for the space is only insulation between trusses and protection is provided above. Is there any restriction on how the insulation is held in place? Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut www.fpdc.com 860.535.2080 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)