I can't seem to find it. However my understanding was that the reason
for the exception was the expectation of the insulation falling on top
of the upright head in this interstitial space and making this head
nothing but a thief from the heads above. Following that logic it seems
that this would only apply if the insulation was expected to fall
quickly in a fire situation. ie: friction or plastic holding it up. I do
not see this in the book but I just keep trying to convince myself that
this was the case.  


Rod DiBona
Vice President
Rapid Fire Protection
[EMAIL PROTECTED]
605-348-2342 ph
605-391-3553 cell

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - FPDC
Sent: Wednesday, March 12, 2008 3:05 PM
To: [email protected]
Subject: insulation and concealed space

NFPA 13 (2002) section 8.14.1.2.13 states that sprinklers may be omitted
from a concealed space if the ceiling for the space is only insulation
between trusses and protection is provided above. Is there any
restriction on how the insulation is held in place?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to