FM recommends 0.15/6,000 for baled Flax and similar fibers up to 16 ft.
high (Data Sheet 8-7). I suspect hay would have similar burn
characteristics; maybe more difficult to burn, as it tends to be
"greener" (I believe). It is my understanding that the larger design
area is due to the burrowing effect of burning bales.

I don't know anything about the ability of hay to absorb water and
expand. This could be an issue to consider from a safety standpoint.
Some baled fibers can expand when wet and push out walls; or wet,
unstable piles could topple onto personnel. Just something that someone
should be considering when arranging the storage.

Mark A. Sornsin, PE 
Fire Protection Engineer 
Ulteig Engineers, Inc. 
Fargo, ND  
701.280.8591
[EMAIL PROTECTED] 
 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ed Cyr
Sent: Sunday, March 16, 2008 4:28 PM
To: American Fire Sprinkler Association
Subject: Hay Bale/Cube Storage

Forum,

 

What commodity class would hay bales in solid piles to 20 feet in height
fall under?

This is a fully enclosed structure.

Thanks in advance,
Ed Cyr

Alpha Fire Sprinkler Corp.



 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to