Speaking of Omegas, I met a fitter this morning that had a tattoo of
an Omega sprinkler on his bicep.
At 11:47 AM 3/26/2008, you wrote:
In response the Omega/GB problem has not gone away since there are
probably thousands that have not been changed out or replaced.
If the industry is really serious about ensuring the residential
systems work just mandate the "Put the Water in the Bucket" test and
do an on the site test that the system delivers the correct water to
the remote sprinklers. It is my understanding that Upnor does that
with each system that is installed. When the "Put the Water in the
Bucket" test was first introduced in Cobb County, GA there were
quite a few systems installed by sprinkler contractors that did not
pass the test. Residential systems should be field tested to insure
that the installation will provide the water and pressure required.
Michael L. Brown
Manager of Technical Services
The Reliable Automatic Sprinkler Company, Inc.'