Sean,
Which edition of 30 are you using?
Todd
At 10:34 AM 4/3/2008, you wrote:
Todd,
Check out NFPA 30, Table 6.8.2.(e).
Sean Conlin
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams
- FPDC
Sent: Thursday, April 03, 2008 8:59 AM
To: [email protected]
Subject: motor oil
I was at a location the other day that had pallets of motor oil
(Class IIIB liquid) in quart and gallon plastic containers stacked 1
high (5 ft). I have never evaluated this specific commodity before so
I started my search from scratch. There seems to be nothing in NFPA
13 that addresses it, so I went to NFPA 30. the but the best I could
find there was small metal containers of IIIB. Since this type of
stuff is all over the place, I would assume that this has had to be
evaluated, but I can't find any resource. Any help?
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
--
No virus found in this incoming message.
Checked by AVG.
Version: 7.5.519 / Virus Database: 269.22.5/1357 - Release Date: 4/3/2008
10:48 AM
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)