the real question is whether it is cheaper to rebuild the bathroom walls to
properly allow the installation of the sheetrock or to add sprinklers.

Garth

----- Original Message ----- 
From: "Todd Williams - FPDC" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Friday, April 11, 2008 3:31 PM
Subject: RE: thermal barrier


The GC figures he can pack a lot of mineral wool
for the price of 90+ sprinklers


At 04:06 PM 4/11/2008, you wrote:
>Todd,  Without sounding smug, wouldn't it be easier to install the
sprinkler ?
>
>John Drucker
>Fire Protection Subcode Official (AHJ)
>
>
>-----Original Message-----
>From: [EMAIL PROTECTED]
>[mailto:[EMAIL PROTECTED]
>  On Behalf Of Todd Williams - FPDC
>Sent: Friday, April 11, 2008 3:40 PM
>To: [email protected]
>Subject: RE: thermal barrier
>
>Do thermal barrier and fire resistance mean the
>same thing? You could put sheet metal on metal
>studs and it would be a non-combustible
>construction would have a certain resistance,
>but would not be a thermal barrier. The
>definition in NFPA 13R give a certain definition
>to thermal barrier and the handbook commentary
>gives notes basically what several people have
>said. However, my situation is a little more complicated (are you
surprised?)
>
>What I am working on is a 90-unit wood frame
>hotel with a 13R system. The original design had
>a modular bathroom, which has been scrapped in
>favor of a stick-built one. The way this is
>framed, a layer of sheetrock cannot be installed
>behind the front and back of the tub (the side
>along the back wall can be). The proposal has
>been made to fill the void space behind the
>cast-iron tub with mineral wool. My question is
>does this provide the required thermal barrier
>and how would I go about proving it?
>
>
>
>At 09:14 AM 4/11/2008, you wrote:
> >Double check that, usually you need "Type X"
> >5/8" to achieve the 1 hr. rating.  According to the IBC it takes two
> >layers, staggered of 1/2"
> >each side to get a 1 hour rating.  See Item
> >14-1.2 in Table 719.1(2).  One layer of 5/8"
> >Type X on each side will also give 1hr, Item 14-1.3.
> >
> >You will most likely be within the 15 minute window with standard 1/2"
> >sheet rock over studs with no exposed combustibles.  Make sure all
> >penetrations into the stud cavity are sealed with fire caulk.
> >
> >Thermal barrier is between the bathroom and the adjacent space.
> >
> >
> >Craig L. Prahl, CET
> >Fire Protection Group
> >Mechanical Department
> >CH2MHILL
> >Lockwood Greene
> >1500 International Drive
> >PO Box 491, Spartanburg, SC  29304-0491 Direct - 864.599.4102 Fax -
> >864.599.8439 [EMAIL PROTECTED] http://www.ch2m.com
> >
> >-----Original Message-----
> >From: [EMAIL PROTECTED]
> >[mailto:[EMAIL PROTECTED] On Behalf Of Eric
> >Tysinger
> >Sent: Friday, April 11, 2008 8:47 AM
> >To: [email protected]
> >Subject: RE: thermal barrier
> >
> >Don't forget the thermal barrier is required behind the fixtures and
> >must extend to the floor even behind the bathtubs. If you need to prove
> >the rating (15min) a simple spec sheet on gypsum board should provide
> >that. Any UL fire rating details will show ½" gypsum on each side of a
> >metal stud wall as at least one-hour.
> >
> >Eric Tysinger
> >Design Manager
> >Wayne Automatic Fire Sprinklers, Inc.
> >
> >
> >-----Original Message-----
> >From: [EMAIL PROTECTED]
> >[mailto:[EMAIL PROTECTED] On Behalf Of Dewayne
> >Martinez
> >Sent: Friday, April 11, 2008 7:35 AM
> >To: [email protected]
> >Subject: RE: thermal barrier
> >
> >I believe a 1/2" sheet of gyp bd meets this criteria but you may want
> >to show him 13R (07)6.9.2.
> >The requirement for the thermal barrier has been removed.
> >Dewayne
> >
> >-----Original Message-----
> >From: [EMAIL PROTECTED]
> >[mailto:[EMAIL PROTECTED]
> >On Behalf Of Todd Williams - FPDC
> >Sent: Friday, April 11, 2008 6:04 AM
> >To: [email protected]
> >Subject: thermal barrier
> >
> >NFPA 13R includes an exclusion for sprinklers in bathrooms less than
> >55 sqft and where the walls behind fixtures "are of non-combustible or
> >limited combustible materials providing a 15-minute thermal barrier".
> >Is there any way to quantify if this criteria is met? A thermal barrier
> >to what? I have an AHJ questioning this.
> >
> >Todd G. Williams, PE
> >Fire Protection Design/Consulting
> >Stonington, Connecticut
> >www.fpdc.com
> >860.535.2080
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >To Unsubscribe, send an email
> >to:[EMAIL PROTECTED]
> >(Put the word unsubscribe in the subject field)
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >To Unsubscribe, send an email
> >to:[EMAIL PROTECTED]
> >(Put the word unsubscribe in the subject field)
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >To Unsubscribe, send an email
> >to:[EMAIL PROTECTED]
> >(Put the word unsubscribe in the subject field)
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >To Unsubscribe, send an email
> >to:[EMAIL PROTECTED]
> >(Put the word unsubscribe in the subject field)
>
>Todd G. Williams, PE
>Fire Protection Design/Consulting
>Stonington, Connecticut
>www.fpdc.com
>860.535.2080
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>To Unsubscribe, send an email to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)
>
>CONFIDENTIAL AND PROPRIETARY:
>This email message is intended only for the use
>of the individual or entity to which it is
>addressed and may contain information that is
>privileged and confidential, nor is it, unless
>specifically stated, intended to be relied upon
>by any person or persons other than the
>individual or entity named above and no
>warranties or representations are made or
>intended to persons or entities not named
>above.  If the reader is not the intended
>recipient, you are hereby notified that any
>dissemination, distribution or copying of this
>communication is strictly prohibited.  If you
>have received this communication in error,
>please notify us immediately by telephone,
>return this message to the address above and delete all copies.  Thank you.
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>To Unsubscribe, send an email to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to