I personally don't design SFDs but have seen sprinkler plans for many of
them (and I stayed at a Holiday Inn last night).  The architectural,
structural, mechanical plans, etc. are generally very simple and lacking the
type of detail you'd expect on a commercial project.  Likewise, the
sprinkler plans tend to be simple - mains & branchlines drawn as nice strait
lines with few or no offsets.  Then you get to the jobsite and, 'Hey,
where'd that duct come from.  Gotta 90 around it."  "Hey, who added the
vaulted ceiling, gotta add a couple 90's to get above it."  

I can think of 2 basic reasons a sprinkler system would fail a bucket test.
1) Out of necessity, the fitter installed more pipe & fittings than the
designer calced for.
2) The underground supply isn't as hydraulically friendly as it's supposed
to be.  Small diameter copper (especially the coiled type) is notorious for
being installed with seemingly minor kinks that restrict water flow.
Pressure losses through meters can be significantly more than many calcs
allow for.

This takes me back to a recent thread concerning code changes that will
require sprinkler installation in all new SFDs.  Just like in Cobb County,
THERE WILL BE A LEARNING CURVE for the new installation contractors
(sprinkler, plumber, or whatever).  Designers need to allow for extra pipe &
fitting.  Installers need to think ahead & coordinate so extra pipe &
fittings are kept to a minimum.  Underground services have to be installed
correctly.  

I personally think bucket tests on 13D installations are a good thing.
Nobody want to do it and nobody wants to fail it.  Unfortunately, as in Cobb
County, it becomes part of the 'training' for designers & installers.  And
when all SFDs require sprinklers, we're going to need a lot of that.

Ed Kramer
Littleton, CO 

> -----Original Message-----
> From: [EMAIL PROTECTED] [mailto:sprinklerforum-
> [EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED]
> Sent: Monday, April 14, 2008 7:50 AM
> To: [email protected]
> Subject: RE: What is a Bucket Test?
> 
> Mike,
> 
> Now we are at the heart of the matter.  If the bucket test results in a
> surprising number of failures, what is the explanation for this?  Is it
> the way the standard is written, is the bucket test technically flawed?
> 
> Seems this would be a great senior research project to figure this out.
> I don't understand a surprisingly high failure rate when system design
> is performed by competent FP firms.
> 
> Bill Brooks
> 
> William N. Brooks, P.E.
> Brooks Fire Protection Engineering Inc.
> 372 Wilett Drive
> Severna Park, MD 21146
> 410-544-3620 Phone
> 410-544-3032 FAX
> 412-400-6528 Cell
> 
> -------- Original Message --------
> Subject: RE: What is a Bucket Test?
> From: "Mike Brown (TECH- GVL)" <[EMAIL PROTECTED]>
> Date: Mon, April 14, 2008 9:28 am
> To: "[email protected]"
> <[email protected]>
> 
> It was surprising the number of systems that failed when the test was
> preformed.
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> To Unsubscribe, send an email to:Sprinklerforum-
> [EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to