SFPE Research Foundation is sponsoring a study and I understand FM will
do additional testing AFTER SFPE's is concluded next year.  Be aware
that some of the HVLS fan manufacturer's literature indicates velocities
below the current FM guidelines, but that is not apples-to-apples and
probably doesn't actually meet FM req's as they stand now.

Unfortunately these fans are common in warehouses and with both ESFR and
control mode sprinklers.

Scott 
 
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Joe
Hankins
Sent: Tuesday, April 15, 2008 7:06 PM
To: [email protected]
Subject: Re: Very Large Ceiling Fans

Dave,

This is a known problem, although there is some controversy swirling 
around.  There are two potential problems: delayed operation of ESFRs 
due to the air movement and obstruction presented by fan blades.
Proposals have been made for 13, but final decisions are awaiting 
testing. The limited testing done so far is not encouraging.  At this 
point, the prudent designer would not consider ESFRs a viable option for

use with "Big Ass (tm)" fans or similar large diameter fans.

Joe

Dave Phelan wrote:
> Good evening all,
>
> I ran into something today on a warehouse inspection that made me
wonder
> ..... This is an ESFR protected warehouse of +- 200,000 sq. feet and
30 foot
> roof height.  They had installed ceiling fans for interior enviroment
> purposes that were about 25 feet in diameter, several throughout the
space.
> These fans run at relatively low blade speed but are rated for upwards
of
> 300,000 CFM.  They do produce a very noticeable breeze without being
> overpowering or noisy.  No swoosh-swoosh sounds like in the 'old
days'.  So
> why do I care .....
>
> What impact would these operating fans and their downward push have on
the
> rising heat plume of a fire, particularly in an ESFR system??  I
called the
> manufacturer and posed just that question.  It seems that the
practical
> implications have not yet been tested but are under consideration.  I
was
> informed that the fans were 'NFPA 13 compliant'.  I asked the
gentleman if
> he knew what that meant and he agreed not really.  I'm willing to bet
that
> was relating to obstruction rules and not element response or head
skipping.
> He also mentioned using shut-offs and fire alarm relays but thats not
going
> to help when the initial waterflow signal is delayed.  I also dont
know of
> any code-leg to stand on if I wanted to push something.  I'm really
looking
> for just some background knowledge.
>
> So I'm wondering if anyone else has run across this issue.  I know
that Tyco
> did testing on residential fan operation and sprinkler response that
did
> indicate downward air movement could delay sprinkler operation.  This
is far
> from a residential fan or system so I'm thinking its magnified that
much
> more.
>
> Thanks.
> Dave P.
> An AHJ in NJ
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
>   

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to