SFPE Research Foundation is sponsoring a study and I understand FM will do additional testing AFTER SFPE's is concluded next year. Be aware that some of the HVLS fan manufacturer's literature indicates velocities below the current FM guidelines, but that is not apples-to-apples and probably doesn't actually meet FM req's as they stand now.
Unfortunately these fans are common in warehouses and with both ESFR and control mode sprinklers. Scott -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Joe Hankins Sent: Tuesday, April 15, 2008 7:06 PM To: [email protected] Subject: Re: Very Large Ceiling Fans Dave, This is a known problem, although there is some controversy swirling around. There are two potential problems: delayed operation of ESFRs due to the air movement and obstruction presented by fan blades. Proposals have been made for 13, but final decisions are awaiting testing. The limited testing done so far is not encouraging. At this point, the prudent designer would not consider ESFRs a viable option for use with "Big Ass (tm)" fans or similar large diameter fans. Joe Dave Phelan wrote: > Good evening all, > > I ran into something today on a warehouse inspection that made me wonder > ..... This is an ESFR protected warehouse of +- 200,000 sq. feet and 30 foot > roof height. They had installed ceiling fans for interior enviroment > purposes that were about 25 feet in diameter, several throughout the space. > These fans run at relatively low blade speed but are rated for upwards of > 300,000 CFM. They do produce a very noticeable breeze without being > overpowering or noisy. No swoosh-swoosh sounds like in the 'old days'. So > why do I care ..... > > What impact would these operating fans and their downward push have on the > rising heat plume of a fire, particularly in an ESFR system?? I called the > manufacturer and posed just that question. It seems that the practical > implications have not yet been tested but are under consideration. I was > informed that the fans were 'NFPA 13 compliant'. I asked the gentleman if > he knew what that meant and he agreed not really. I'm willing to bet that > was relating to obstruction rules and not element response or head skipping. > He also mentioned using shut-offs and fire alarm relays but thats not going > to help when the initial waterflow signal is delayed. I also dont know of > any code-leg to stand on if I wanted to push something. I'm really looking > for just some background knowledge. > > So I'm wondering if anyone else has run across this issue. I know that Tyco > did testing on residential fan operation and sprinkler response that did > indicate downward air movement could delay sprinkler operation. This is far > from a residential fan or system so I'm thinking its magnified that much > more. > > Thanks. > Dave P. > An AHJ in NJ > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)