Sean,

Since this thing is already calced, and since you'd have to pipe
schedule all the way to the source (street connection or tank), and
since unless calculations prove otherwise all UG feeds must be at
least 6" wouldn't it just be easier and less costly to calc it?

On 4/18/08, Sean Conlin <[EMAIL PROTECTED]> wrote:
> Good day forum members,
>
>
>
>  Are there any restrictions on providing a tail-end preaction-based pipe
>  schedule system connected to a hydraulically calculated system?
>
>
>
>  The renovation is a 24'x24' computer room addition, re-routing the existing
>  wet pipe lines around the room, and providing a preaction system connected
>  to the existing system cross main.
>
>
>
>  Any thoughts are appreciated.
>
>
>
>  Sean Conlin
>
>  Demand Sprinkler Design Inc.
>