Ip of 1.0 is for the "structure". 

NFPA 15 reverts to 13 for bracing issues.


Craig L. Prahl, CET   
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Monday, April 21, 2008 3:00 PM
To: [email protected]
Subject: Re: Seismic bracing of sprinkler pipng in exterior tank farm

Craig,

Are you sure about the importance factor (Ip) being 1.0?  In most of the
work I've seen regarding fire sprinkler systems that value is 1.5.

Also, what does the latest edition of NFPA-15 say?  I'm just jumping to
the conclusion of course that it's a fixed waterspray system.

Interesting to be sure.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website



[EMAIL PROTECTED] wrote:
> I have a tank farm with deluge sprinkler protection on the vessels, 
> steel pipe rack and supporting steel.  The debate that has arisen is 
> whether this type of arrangement really needs to be seismically
braced.
> The issue is that it is not a structure, and not occupied.  However
the
> materials within the tanks are flammable/combustible.   
>
> Now to what degree of seismic resistance the structural steel and tank

> supports are designed to is unknown.
>
> Is there an exemption for this type of installation?  Based on the 
> information provided by structural, the occupied buildings would be 
> braced, no question there.  But for exterior vessels, that is the 
> question.
>
> Soil Site Class = D
> Occ. Class. = I
> Seis. Des. Cat. = D
> Structure Ip = 1.0 but might be argued to be 1.25 (Occ. Class II)
>
> Craig L. Prahl, CET   
> Fire Protection Group
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491 Direct - 864.599.4102 Fax - 
> 864.599.8439 [EMAIL PROTECTED] http://www.ch2m.com
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email 
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
>
>   
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to