In terms of codes and standards, there's no reason the floor controls
can't be in the mechanical room.   But I'd run it by all the AHJ's
first.

Steve Leyton
Protection Design & Consulting


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Joe
Powell
Sent: Wednesday, April 23, 2008 6:58 AM
To: [email protected]
Subject: FW: Floor Control Valve Locations

The fire service rises up into the mechanical room.  The building is a
three
story with manual wet Class 1 standpipes.  The mechanical rooms are
stacked
on all three floors.  Is it acceptable to locate the floor control
valves to
be located in the mechanical rooms rather than on the standpipes in the
remote stairwells?  Aren't floor control valves for maintenance rather
than
fire dept. use?

 