You're right Rahe, flow must be modulated after the venturi or pretty much
any other flowmeter including the ones I use.  Mine have a transducer paddle
wheel (like a boat's speedo) that spins on flow once programmed to the size
of the pipe.  One additional bonus to these is they can be programmed to
read between any pipe size from 1" to 10", can be calibrated to 1 to 3
points, can total the flow used and be programmed to read single digits,
increments of 5 or 10 or whatever and also to read in different increments
at different flow rates.  I have Powhaton globe valves on the discharge end
of the tubes, I've found them to be the most able to adjust and hold a
setting while flowing.  I have mine read in increments of 1 up to 300 GPM
and then switch to increments of 5 to 750 and them light an overlimit signal
above that (accuracy fails at 800+ with a 2 1/2" size).

Tom Duross


The real problem with flow meters is that there has to be a true laminar
flow through the venturi to be even close to accurate and that the flow
meter has to be calibrated before any testing can be done through it per
NFPA 25.  If you have ever tried to measure flow through one of the
commercially available flow meters, you will find yourself trying to guess
or average the jittery needle movement.

They are not as accurate as a pitot gauge when calibrated and properly
used.  In my jurisdiction I do not allow them to be installed or used for
flow testing.

Thank You

Rahe Loftin, P.E.

Chris the only "In-Line" Flow meter we've used is on fire pumps and we use
the Victaulic Style 735 (Sizes 2.5 to 10" 500Psi max)
Thom McMahon