Trick question huh? Some would argue reversing the FDC check, and flowing
there from..

R/

Matt

Matthew J. Willis
Living Water Fire Protection, LLC.
1160 McKenzie Rd.
PO Box 877
Cantonment, FL. 32533
850-937-1850 Voice
850-937-1852 Facsimile
[EMAIL PROTECTED]
 

----- >-----Original Message-----
----- >From: [EMAIL PROTECTED] 
----- >[mailto:[EMAIL PROTECTED] On 
----- >Behalf Of Fletcher, Ron
----- >Sent: Friday, May 30, 2008 10:47 AM
----- >To: [email protected]
----- >Subject: RE: 200 psi test for components rated 175
----- >
----- >six 
----- >
----- >-----Original Message-----
----- >From: [EMAIL PROTECTED]
----- >[mailto:[EMAIL PROTECTED] On 
----- >Behalf Of Gregg Key
----- >Sent: Friday, May 30, 2008 8:37 AM
----- >To: [email protected]
----- >Subject: Re: 200 psi test for components rated 175
----- >
----- >Speaking of such test, How many systems are installed 
----- >with a means to test the backflow at the required 
----- >forward flow rate? like a wall hydrant?
----- >
----- >Thom McMahon wrote:
----- >> Don't forget the derided full forward flow test!
----- >> 
----- >> -----Original Message-----
----- >> From: [EMAIL PROTECTED]
----- >> [mailto:[EMAIL PROTECTED] On 
----- >Behalf Of Steve 
----- >> Leyton
----- >> Sent: Friday, May 30, 2008 8:42 AM
----- >> To: [email protected]
----- >> Subject: RE: Re[2]: 200 psi test for components rated 175
----- >> 
----- >> So it's contractual, not philosophical.   Presumably, 
----- >the installing
----- >> contractor tests it ... 
----- >> 
----- >> I don't think we're talking about testing the backflow 
----- >appliances 
----- >> itself for functionality - that's best left for the "certified
----- >backflow
----- >> technician."   If you pump up an UG including the BFP, 
----- >the relief
----- >valve
----- >> will only operate when there's a differential between 
----- >the clappers.  
----- >> So an RPZ or RPDA usually weeps a bit when you pump it 
----- >up, but once 
----- >> the line is equalized you can run a conventional 
----- >hydro.  And if you 
----- >> just want to test against it, you can pump up through 
----- >the FDC or main 
----- >> drain or the supply-side tap on the riser check, if so 
----- >equipped.
----- >> 
----- >> Steve Leyton
----- >> Protection Design & Consulting
----- >> 
----- >> 
----- >> -----Original Message-----
----- >> From: [EMAIL PROTECTED]
----- >> [mailto:[EMAIL PROTECTED] On 
----- >Behalf Of Coastal
----- >> Sent: Thursday, May 29, 2008 7:10 PM
----- >> To: Steve Leyton
----- >> Subject: Re[2]: 200 psi test for components rated 175
----- >> 
----- >> Hello Steve,
----- >> 
----- >> I start 1' AFF with my work. I sub out any underground 
----- >installation 
----- >> work I get (which I try to avoid) and it is up to them 
----- >to test it.
----- >> Only question I have is how do you get an RPZ to hold the back 
----- >> pressure to hydro to it? Pump the system up through 
----- >the #1 test cock?
----- >> 
----- >> --
----- >> Best regards,
----- >> Charles Thurston 
----- >>  Coastal                            
----- >mailto:[EMAIL PROTECTED]
----- >> 
----- >> Thursday, May 29, 2008, 6:55:37 PM, you wrote:
----- >> 
----- >>> I'll bite - why not?   If the Fire Department pumps 
----- >into the FDC,
----- >> isn't
----- >>> it likely to back pressure the BFP to at least 150?  
----- >And if so,
----- >> wouldn't
----- >>> it be prudent to test the assembly?
----- >> 
----- >>> Steve Leyton
----- >>> Protection Design & Consulting
----- >> 
----- >> 
----- >>> -----Original Message-----
----- >>> From: [EMAIL PROTECTED]
----- >>> [mailto:[EMAIL PROTECTED] On 
----- >Behalf Of 
----- >>> Charles Thurston
----- >>> Sent: Thursday, May 29, 2008 3:30 PM
----- >>> To: IPA
----- >>> Subject: Re: 200 psi test for components rated 175
----- >> 
----- >>> Hello IPA,
----- >> 
----- >>> I for one have never put 200 on the backflow, I will 
----- >not either.
----- >> 
----- >>> Thursday, May 29, 2008, 6:03:25 PM, you wrote:
----- >> 
----- >>>> I've got this question posed to me:
----- >> 
----- >>>> Backflow preventor is rated at 175 (as are most of the fire 
----- >>>> sprinkler
----- >>>> components) yet we are required to do a 200 psi 
----- >test. Is the keyword
----- >>> here
----- >>>> "working pressure" of 175 psi or am I missing something?
----- >> 
----- >>>> thx,
----- >>>> _______________________________________________
----- >>>> Sprinklerforum mailing list
----- >>>> [email protected]
----- >>>> 
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >> 
----- >>>> To Unsubscribe, send an email
----- >>> to:[EMAIL PROTECTED]
----- >>>> (Put the word unsubscribe in the subject field)
----- >> 
----- >> 
----- >> 
----- >> _______________________________________________
----- >> Sprinklerforum mailing list
----- >> [email protected]
----- >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >> 
----- >> To Unsubscribe, send an email
----- >> to:[EMAIL PROTECTED]
----- >> (Put the word unsubscribe in the subject field) 
----- >> _______________________________________________
----- >> Sprinklerforum mailing list
----- >> [email protected]
----- >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >> 
----- >> To Unsubscribe, send an email
----- >> to:[EMAIL PROTECTED]
----- >> (Put the word unsubscribe in the subject field)
----- >> 
----- >> _______________________________________________
----- >> Sprinklerforum mailing list
----- >> [email protected]
----- >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >> 
----- >> To Unsubscribe, send an email
----- >> to:[EMAIL PROTECTED]
----- >> (Put the word unsubscribe in the subject field)
----- >> 
----- >> 
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email 
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field)