Jaber,

If they are really concerned, look into a double-interlock pre-action system. That would be about the best way to bring the chance of accidental discharge to a minimum. Considering you e-mail address, should I assume this is outside the United States? What do the local codes say about replacing sprinklers with a chemical agent?


At 08:44 AM 6/23/2008, you wrote:
Newly constructed research and development lab facility is protected by a wet type sprinkler system, one of the lab scientist is worried about the accidental release of the automatic sprinkler heads on top or in the vicinity of the high tech., expensive analytical instruments such as NMR, FTMS, autospec GC/MS and ESEM , which present a potential risk of damage to these instruments in case these sprinklers kick off during actual emergency or broken by mistake by a maintenance personnel or a lab personnel. He suggests gas suppression instead. I explained to him that accidental leakage of wet type sprinkler system is very minimal. The question is what the probability of activation and how much will it cost to replace the existing system with a gas suppression system. Your recommendations/insights are highly appreciated.
Jaber Al-Haji
[EMAIL PROTECTED]
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080 _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to