Brian,

I believe it should be read to mean that the most/furthest away you have to be is a maximum of 36-in. The 36-in. is the maximum limit. Without this provision, you would instead need to be 4 times away or 96-in.


Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)

This e-mail and any attachments are CONFIDENTIAL and may be protected by one or more legal privileges. It is intended solely for the use of the addressee identified above. If you are not the intended recipient, any use, disclosure, copying or distribution of this e-mail is unauthorized. If you received this e-mail in error, please notify the sender immediately at the above captioned address. ----- Original Message ----- From: "Brian Harris" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Monday, July 14, 2008 1:36 PM
Subject: Sprinkler Pattern Obstructions


Forum,
I know I must be reading this wrong but as usual I am in a hurry and could
use some help. NFPA-13 (2007) 8.8.5.2.1.3 states that the sprinkler shall be
positioned a minimum of 4 times the maximum dimension of the obstruction,
but then it goes on to say a maximum of 36" clear space. In my case I have a
24" column I'm trying to avoid which by the 4 times rule would get me 8'
away, how does the max. 36" clear come into play? Also look at Figure
8.8.5.2.1.3, I'm so confused ........


Regards,


<http://www.firstdefensefire.com/>








E-mail message checked by Spyware Doctor (6.0.0.354)
Database version: 5.10250e
http://www.pctools.com/en/spyware-doctor-antivirus/



--------------------------------------------------------------------------------


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to