You will need a screen box with removable 1/2" mesh brass or stainless steel
screens to keep out fish, frogs and grass from the pump sump. See NFPA 20
for the screen size. It is based on fire pump size - gpm relates to screen
area below the water line.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bobby
McCullough
Sent: Tuesday, July 22, 2008 10:02 AM
To: [email protected]
Subject: Structure for Vertical Pump

We will be installing a vertical fire pump taking suction from a pond in
the south east corner of Georgia.  The general contractor needs
assistance with the design of the structure, possibly from someone on
the structural side.  Any suggestions I can pass along?