Heres the IBC (which are mimicked in the IFC) code references; 2006 IBC 905.4 Location of Class 1 Standpipe Hose Connections provides; "Class I standpipe hose connections shall be provided in all of the following locations; 1. In every required stairway.............
2006 IBC 1020.1.2 Penetrations provides; "Penetrations into and openings through and exit enclosure are prohibited except for required exit doors................, sprinkler piping, standpipes................ 2006 IBC 905.3 Required Installations also provides; "Standpipe Systems are allowed to be combined with automatic sprinkler systems". Keep in mind that the aforementioned must be located such not to impede or diminish the required egress width of the stairway/stairway landings pursuant to 2006 IBC 1009.1 and 1009.4. Hope that helps John Drucker Fire Protection Subcode Official (AHJ) Red Bank, New Jersey _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)