Maybe. 

Floor coverings, specifically carpet is considered interior finish
pursuant to 2006 IBC 804.4 and as such Class I (I-1 and I-2) , Class II
materials (A,B,E,H,I-4,M,R-1,R-2 and S) and DOC FF-1 compliant in all
the others. The exception allows interior finish requirements to be
bumped down one grade where a building is equipped throughout with an an
automatic sprinkler system in accordance with 2006 IBC 903.3.1.1 or
903.1.2.   903.3.1.1.1 -4. Exempts "In rooms or areas that are of non
combustible construction with wholly non combustible contents".

So if the interior finish materials meet the non combustible criteria
then sprinklers are only required at the top and bottom levels of a non
combustible stair.  Someones got to go back to the carpet manufacturer
for the answer.

PS, Change Stair Shaft to Stair Enclosure.

Hope that helps

John Drucker
Fire Protection Subcode Official (AHJ, not a scientist ;-))
New Jersey

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Margaret
Zabel
Sent: Thursday, July 31, 2008 11:39 AM
To: Sprinkler Forum
Subject: Stair shafts

Using NFPA 13-2002, paragraph 8.14.3.2 describes the requirements for
sprinklers in non-combustible stair shafts.

Would a non-combustible construction stair shaft (concrete stairs,
sheetrock/rated walls) that has carpet on the landings and stair treads
be considered "non-combustible"?  Assuming the stairs are over 4'-0
wide, should there be sprinklers located throughout the shaft -- below
treads and stairs?

Thank you,

Margaret Zabel
Cisco Fire Sprinklers
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or entity to 
which it is addressed and may contain information that is privileged and 
confidential, nor is it, unless specifically stated, intended to be relied upon 
by any person or persons other than the individual or entity named above and no 
warranties or representations are made or intended to persons or entities not 
named above.  If the reader is not the intended recipient, you are hereby 
notified that any dissemination, distribution or copying of this communication 
is strictly prohibited.  If you have received this communication in error, 
please notify us immediately by telephone, return this message to the address 
above and delete all copies.  Thank you.


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to