I use dry pendent or dry sidewall at top of stack installed 1'-0" down from
deck where duct exits the roof.



Bryan A. Dann
Dannba Design Services, LLC
Fire Sprinkler Designs
Office: (740) 363-5878
Cell: (740) 803-0967
[EMAIL PROTECTED]



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ryan Hinson
Sent: Wednesday, August 27, 2008 1:38 PM
To: [email protected]
Subject: Small orifice sprinkler use in paint booth exhaust duct


Can I use a small orifice head in the exhaust stack of a paint booth in lieu
of 11.2K heads that are in the rest of the booth 14' below to balance the
calcs?  A larger orifice head draws too much water to make the calcs
workable.  NFPA 13(2002) 8.3.4 alludes only to explicitly allowable use in
light hazard occupancies on wet systems.  Does this head have to be an
upright at the top of the stack(which is 4' in diameter, vertically
oriented, and about 11' in length with a rain cover over the top), or can it
be a SDWL installed in the middle or near the bottom?  The required location
this head is driving the whether this system can be wet or not.

 

Thank you,

 

Ryan L. Hinson, Nicet III

Design Manager

Fire Construction Design Services, LLC #C124

A Division of Fire Construction Services, Inc.

6950-43rd Avenue SE

St. Cloud, MN 56304

Direct:  320-250-5404 

Fax: 320-358-3495

email:   <mailto:[EMAIL PROTECTED]>
[EMAIL PROTECTED]

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to