2003 IFC A-4 is classification for arenas 903.2.1.4 Group A-4. An automatic sprinkler system shall be provided for Group A-4 occupancies where one of the following conditions exists: 1. The fire area exceeds 12,000 square feet (1115m2); 2. The fire area has an occupant load of 300 or more; or 3. The fire area is located on a floor other than the level of exit discharge. Exception: Areas used exclusively as participant sports areas where the main floor area is located at the same level as the level of exit discharge of the main entrance and exit.
Noreen -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon Sent: Thursday, August 28, 2008 5:39 PM To: [email protected] Subject: IBC 2003 exemption for sprinklers I remember that there was an exemption for sprinklers over the pool area (Water) or arena area's ( horse arena's) in the IBC an I'm just not finding it. Anyone know what section I need to look at? Thanks in advance for any help. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)