A-4 is classification for arenas

903.2.1.4 Group A-4. An automatic sprinkler system shall be provided for
Group A-4 occupancies where one of the following conditions exists:
1. The fire area exceeds 12,000 square feet (1115m2);
2. The fire area has an occupant load of 300 or more;
or
3. The fire area is located on a floor other than the
level of exit discharge.
Exception: Areas used exclusively as participant sports areas where the
main floor area is located at the same level as the level of exit
discharge of the main entrance and exit.


Noreen 
 
 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Thursday, August 28, 2008 5:39 PM
To: [email protected]
Subject: IBC 2003 exemption for sprinklers

I remember that there was an exemption for sprinklers over the pool area
(Water) or arena area's ( horse arena's) in the IBC an I'm just not
finding
it.

 

Anyone know what section I need to look at?

 

Thanks in advance for any help.

 

Thom McMahon, SET

Firetech, Inc.

2560 Copper Ridge Dr

P.O. Box 882136

Steamboat Springs, CO 80488

Tel:  970-879-7952

Fax: 970-879-7926

 

 

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to