I recall requiring A.S. below an FRP tank if it was more than 18" above the
floor, too.

For those that missed it awhile ago, you can read any current and some older
editions of any NFPA standard by going to nfpa.org, about the code, and then
scroll to the bottom of your selected standard and click on Preview This
Standard or similar wording. You can't copy, cut and paste, print, but you
can read to your heart's content. And for free, what did you want?

glc

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ed Vining
Sent: Wednesday, September 03, 2008 1:52 AM
To: [email protected]
Subject: Re: NFPA 22, 2008 edition

11.6.3 Fiberglass-reinforced plastic (FRP) tanks located inside a building
shall be protected by automatic sprinklers in accordance with ordinary
hazard Group 2 occupancies.

11.6.3.1 Where the hazard is greater than OH2, protection shall be in
accordance with NFPA
13<javascript:parent.loadDoc('/nfpa0001-0049/0013',%20'',%20'codes-13')>.



If you want more, just holler.


Ed Vining


On Tue, Sep 2, 2008 at 9:33 PM, A.P.Silva <[EMAIL PROTECTED]> wrote:

>
> Does anyone have access to the 2008 edition of NFPA 22? If so, can you
> please give me the section 11-6.3?
>
> Thanks,
>
> Tony
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [EMAIL PROTECTED]
>
> To Unsubscribe, send an email
to:[EMAIL PROTECTED]<[EMAIL PROTECTED]
sprinkler.org>
> (Put the word unsubscribe in the subject field)
>



-- 
Ed Vining
4819 John Muir Rd
Martinez CA 94553
925-228-8792
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to