Hi Thom,

Do you know if ACI 318-05 requires anchors be tested in cracked
concrete? Hilti referenced ACI 318-08 as the driving force for testing
anchors in cracked concrete. I'm trying to find a copy ACI 318-05, the
05 edition is referenced by IBC 2006, so far no luck.

If this applies to seismic loads wouldn't we still be able to use HDI's
for hangers and just use the TZ for EQB attachments?

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Monday, September 08, 2008 1:30 PM
To: [email protected]
Subject: RE: The sky is falling

Apparently this is driven by the 2006 IBC. The 2006 changed the system
of
testing for mechanical fasteners, you can check their (IBC) web site for
approved fasteners. This is mechanical fasteners only. The TZ has been
tested and approved. The 2006 has no criteria for testing Power driven
studs, and I believe says "Outside the scope" of this document or
outside
scope for seismic, something like that. Hilti has not tested the HDI or
HDI-P to the new criteria yet, so they are not approved by the building
code
where 2006 is applicable.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Monday, September 08, 2008 1:45 PM
To: [email protected]
Subject: The sky is falling

Anyone else out there heard from Hilti about no longer using their HDI
to
hang pipe from the bottom of cracked concrete in seismic categories C-F?
We
had a (the sky/pipe is falling) presentation from Hilti about using
their
new TZ Kwik Bolt instead of the HDI, HDI-P or powder drive pins. They
leave
you with the impression that all pipe supports must be changed to the
TZ,
they even sighted two projects in AZ where the contractors had to
abandon
the installed HDI's and reinstall the TZ.

I have been doing some research on their presentation and I don't think
their claims will stand the light of day but I would like some other
opinions. I would be glad to PM Hilti's power point presentation to any
interested parties.

I wonder if the marketing guru that got backflows required on Class 1 &
2 sprinkler systems went to work for Hilti?

Ron Fletcher
Aero Automatic
Phoenix, AZ
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to