Hello Bob,

I'll try, I have done Dry Chem in the MAACO paint booths.
See below

Wednesday, September 24, 2008, 5:22:41 PM, you wrote:

>   
> Any takers? I need the help.

> Thanks,

> Bk

> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Bob Knight
> Sent: Wednesday, September 24, 2008 11:47 AM
> To: [email protected]
> Subject: Spray Paint Booth

> Forum,
> I have a couple of questions in regards to spray paint booth for a MAACO
> facility.

> 1)  The spray paint booth has an interior dimension of 13'1".  Are two
> branch lines required, or can one be used?  Per 13 EH max is 12', is there
> anyway to use one line?

The one 3 blocks from here is only 12'0" inside the booth, Check where the
13'1" came from

> 2)  This booth has a plenum between the top of its structure and the
> interior ceiling.  This plenum is for air intake.  Per NFPA 33 air
> recirculation units are to be protected.  Does the air intake fall into this
> category, and will it require sprinklers?

Is this a heated air booth? If so you will have a heater upstream and yes it
needs to be protected between the heater and the booth, But not upstream of
the heater with Dry Chem. If there is not a heater it is not
protected. Yes fuel to the heater has to shutoff at discharge time.

> 3)  This booth has booth intake and exhaust ducts.  Do both types need
> sprinklers or only the exhaust?

See #2

> Thanks for all your help,

> Bob Knight, CET
> (208) 495-2057
> [EMAIL PROTECTED]
> www.firebyknight.com

> No virus found in this outgoing message.
> Checked by AVG - http://www.avg.com 
> Version: 8.0.169 / Virus Database: 270.7.1/1688 - Release Date: 9/24/2008
> 6:29 AM

> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [EMAIL PROTECTED]

> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)


-- 
Best regards,
 Charles Thurston                            mailto:[EMAIL PROTECTED]
  Coastal Fire Protection

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to