Be careful here. Know what the temperatures will be both in the ground where the pipe runs and where something like a hydrant comes up out of the ground. PVC strength decreases rapidly with temperature. There might also be daily temperature swings larger than at more typical installations. Connections may be where you may have the problems. BTW, SS hardware rots out DI. Check the technical papers at www.ebaa.com/engineering.htm# for more information. The FM approved HDPE is probably the best, but again pay attention to how you are connecting it to something else and what the protection should be for those parts.

Allan Seidel
St. Louis, MO

On Sep 27, 2008, at 10:30 AM, Scott A. Futrell wrote:

Research HDPE. Probably more cost effective for long runs as well as corrosion resistant and long life. Driscopipe. FM approved.

Scott Futrell

C: (612) 759-5556
W: (763) 425-1001
[EMAIL PROTECTED]
-----------------------------------------------
Sent from a handheld, please excuse any misspelled words.

-----Original Message-----
From: "[EMAIL PROTECTED]" <[EMAIL PROTECTED]>
To: "AFSA Forum" <[email protected]>
Sent: 9/27/08 10:04 AM
Subject: Re: which pipe is right for underground bury in very hot soil?

Suggest C-900 PVC pipe, CL 150 or 200. Ductile iron push-on or MJ fittings, with SS hardware that in turn is coated with non-oxide grease. ALL ferrous joints then enveloped with seamless polyethylene sleeves and heavily taped at each end. 75 years? Who knows, but we've had success with these practices with very hot soils in SoCal, in areas that were experiencing blowouts from corrosion.

Steve L.


Sent from my Verizon Wireless BlackBerry

-----Original Message-----
From: ... .... <[EMAIL PROTECTED]>

Date: Sat, 27 Sep 2008 02:21:20
To: <[email protected]>
Subject: which pipe is right for underground bury in very hot soil?


Underground Question:
we have got
soil that is alkaline hot.
and hot temperatures too
in a desert with too few
days below 100 F.
what we have is
miles of underground to install around
this campus. and cost savings is
not one of the issues.
longevity of service is.
would ductile iron protected with tar or PE wrapper
be preferred
to simply PVC?
or is another pipe option,
 a better bet on
 reaching 75 years?

service life desired: 75 years
diameter: 8 inch
depth of bury 3+ feet

scot deal
excelsior fire engineering
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum <http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum> For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:Sprinklerforum- [EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

__________ Information from ESET NOD32 Antivirus, version of virus signature database 3475 (20080926)__________
The message was checked by ESET NOD32 Antivirus.
http://www.eset.com <http://www.eset.com>

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:Sprinklerforum- [EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to