Well actually there is ONE reference in the codes for using spray sprinklers and glass. It is in NFPA 101 - Life Safety Code under Atriums and applies to a 1 hr separation. The trick there is ensuring the set-up is "wetting the entire surface". From this humble beginning, it has been a common practice to apply it elsewhere.

Roland

On Sep 30, 2008, at 6:02 AM, Chris Cahill wrote:

Cause there is nothing in the code that I am aware of that gives a rating with ordinary sprinklers at any spacing. The 6' comes in about openings in
floors and as an alternate in the atriums.  These are two specific
situations addressed but not a general 1 hr rating. The floor opening has nothing to do with ratings and the atrium needed a solution to rating before
the development of the Tyco heads once code officials decided to allow
multiple floors to be connected without a traditional rating.

Tyco heads are listed and tested to the same standard as other rated
construction methods for ratings. It's the same test for sheetrock and concrete. If you have a corridor that requires a rating Tyco heads are the
only code complying solution I am aware of if using sprinklers.

And to Craig's comment if it's unrated then you don't need any sprinklers on
the glass.

Of course standard note and discussion point regarding a contractor choosing methods of rating vs. the architect and engineer who should have specified
methods.

Chris Cahill, P.E.