Dewayne,

Thanks, that's what I was thinking and hoping for was to treat it as
obstructed construction w/low sprinklers. I just wanted to be sure I wasn't
missing anything.

Any other opinions on this?

Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731) 424-0130 office
(731) 267-4853 cell
     
 
 
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dewayne
Martinez
Sent: Thursday, October 16, 2008 9:01 AM
To: [email protected]
Subject: RE: Combust. Concealed Space

Bobby,
I would treat it as obstructed construction with your sprinklers located
1-6in below the bottom of the joists.
You wouldn't need sprinklers in each pocket if the insulation wasn't
there so I do not see why you would need additional sprinklers with the
insulation.  Now if the ceiling is installed within 6in from the bottom
of the wood joists, you can omit the sprinklers in the combustible
concealed space entirely per 8.15.1.2.5.  Just my take on it....
Dewayne

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bobby
Gillett
Sent: Thursday, October 16, 2008 8:32 AM
To: [email protected]
Subject: Combust. Concealed Space

I am working on a two story building with a dry system. First floor
ceiling is 2x4 ACT @ 8'-0 hung from the bottom of the 2x12 joists. There
is mesh netting at the bottom of the joists supporting the insulation.
There is plywood decking at the top of the joists used as subfloor for
second floor.
The 2x12 joists are on 16" centers. I'm waiting for the answer on the
thickness of the insulation.

 

If I'm reading correctly, NFPA 2007 8.15.1.2.16 allows me to not
sprinkle the area between the ceiling and bottom of joists if there are
sprinklers above the insulation. But being these are joists and not
trusses that creates many, many sprinklers. Is there anything that would
allow sprinkling below the insulation and not above? I have asked the GC
for proposed thickness of insulation and the possibility of raising the
insulation to the bottom of deck so there would only be one space. I
don't have a reply as of yet.

 

Bobby Gillett

SR.Project Manager

[EMAIL PROTECTED]

(731) 424-0130 office

(731) 267-4853 cell

   

 

 

 

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)