I just got a copy of the insurance plan that FM developed when that
was their risk back in the 1980s. The underground they showed was
more convoluted than I thought. Taking that in to consideration, we
need 1558 gpm at 311 psi to make the .45/2500. I had the sublime
pleasure of breaking this news to the facilities manager today.
At 01:12 PM 10/20/2008, you wrote:
I can hear Joe's eyes rolling from here.
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams
- FPDC
Sent: Wednesday, October 15, 2008 11:51 AM
To: [email protected]
Subject: RE: Placard fact check
This section of the building was built in the 1950s and was all pipe
schedule. At some point, some one allegedly did hydraulics (due to
the rack storage) and this is where the placard came from. There have
been at least 5 owners that I am aware of. When and how this was done
is beyond me. As far a due diligence, the last time I saw an FM
Global guy on a job, he was training someone new in hydraulics. His
line was "Ignore the riser nipples, they don't have any impact. Just
include the elevation." I doubt if many insurance companies actually
do hydraulics before they write a risk; they just look at the placards.
At 11:25 AM 10/15/2008, you wrote:
>I wonder what the inspectors were doing when they reviewed the info on
>the hydraulic placard simple math and some common sense would have
>indicated that something was wrong. The density 0.45 gpm per sq. ft.
>times the area of operation 2,500 sq. ft. times 1.3 (30% increase for
>hydraulic inefficiency of tree system) indicates a flow requirement of
>1,462.5 rounded up to 1,465 gpm for the system. It appears that the
>hydraulic placard was based on the design density multiplied by area of
>operation plus 100 gpm.
>
>What happened to the HPR carriers plan review of the shop drawings and
>hydraulic calculation or due diligence when taking over the account from
>another carrier.
>
>I hope that the sprinkler contractor doing the annual inspection is
>following NFPA 25 to the letter and not using any "modified" version of
>the NFPA 25 inspection form.
>
>Just goes to show that you must verify all info given to you.
>
>
>Jim Davidson
>
>Davidson Associates
>302-994-9500
>-----Original Message-----
>From: [EMAIL PROTECTED]
>[mailto:[EMAIL PROTECTED] On Behalf Of Todd
>Williams - FPDC
>Sent: Wednesday, October 15, 2008 10:15 AM
>To: [email protected]
>Subject: Placard fact check
>
>This weeks crisis, so far.......
>
>I am working on a plant in MA where they need to add in rack
>sprinklers. The existing ceiling system is a pipe schedule and the
>placard at the riser says it can deliver .45/2500 at a flow of 1220
>gpm at 52 psi. It seemed light, but I don't jump 'til I crunch the
>numbers. In actuality, it requires 1558 gpm at 286 psi at the supply.
>Everybody, including the HPR carrier, has bought into the numbers on
>the riser. Now the excrement is about to impact the vortex generator.
>
>Moral of the story; don't believe everything you read.
>
>Todd G. Williams, PE
>Fire Protection Design/Consulting
>Stonington, Connecticut
>www.fpdc.com
>860.535.2080
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to:
>[EMAIL PROTECTED]
>
>To Unsubscribe, send an email
>to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)
>
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [EMAIL PROTECTED]
>
>To Unsubscribe, send an email to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)