One additional issue to keep in mind is required ventilation,
specifically testing and balancing. Its important to confirm with the
mechanical engineer that said objects will not effect mechanical
operation pursuant to 2003/2006 IMC 403.1(ventilation) & 403.3.4
(balancing)

John Drucker
Fire Protection Subcode Official
Building/Fire/Electrical Inspector 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Noreen H.
McMahon
Sent: Thursday, October 23, 2008 4:32 PM
To: [email protected]
Subject: RE: Fire Sprinkler Pipe through Mechanical Duct

You can pass a pipe through a regular duct, but not 'hazardous' exhaust
ducts (grease, fume hood, flue, etc)  SMACNA (Sheet Metal and Air
Conditioning Contractors National Association) even has a standard
detail on how to deal with a pipe penetrating ductwork in the HVAC Duct
Construction Standards, Metal & Flexible (1995, with Addendum 1,
11/1997) on page 2.10, figure A


Noreen McMahon

 
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Gregg
Fontes
Sent: Thursday, October 23, 2008 10:44 AM
To: [email protected]
Subject: Fire Sprinkler Pipe through Mechanical Duct

After review of NFPA 13, I cannot find a section that prohibits fire
sprinkler pipe from passing through mechanical duct.  Does anyone know
of something in the Mechanical Code that would prohibit steel fire
sprinkler pipe from passing through mechanical ductwork?  Case in point,
2 1/2"
fire
sprinkler line passing through a +/-60" square duct.  Mechanical
contractor
would seal the penetrations.   

Thanks,
Gregg Fontes
Cen-Cal Fire Systems, Inc.
(209)334-9119
 

This email was scanned by D&G Technology Group Secure Scan and found to
contain no virus or harmful content.
Checked by AVG. 
Version: 7.5.549 / Virus Database: 270.8.2/1740 - Release Date:
10/22/2008
7:24 PM
 

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or entity to 
which it is addressed and may contain information that is privileged and 
confidential, nor is it, unless specifically stated, intended to be relied upon 
by any person or persons other than the individual or entity named above and no 
warranties or representations are made or intended to persons or entities not 
named above.  If the reader is not the intended recipient, you are hereby 
notified that any dissemination, distribution or copying of this communication 
is strictly prohibited.  If you have received this communication in error, 
please notify us immediately by telephone, return this message to the address 
above and delete all copies.  Thank you.

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to