One additional issue to keep in mind is required ventilation, specifically testing and balancing. Its important to confirm with the mechanical engineer that said objects will not effect mechanical operation pursuant to 2003/2006 IMC 403.1(ventilation) & 403.3.4 (balancing)
John Drucker Fire Protection Subcode Official Building/Fire/Electrical Inspector -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Noreen H. McMahon Sent: Thursday, October 23, 2008 4:32 PM To: [email protected] Subject: RE: Fire Sprinkler Pipe through Mechanical Duct You can pass a pipe through a regular duct, but not 'hazardous' exhaust ducts (grease, fume hood, flue, etc) SMACNA (Sheet Metal and Air Conditioning Contractors National Association) even has a standard detail on how to deal with a pipe penetrating ductwork in the HVAC Duct Construction Standards, Metal & Flexible (1995, with Addendum 1, 11/1997) on page 2.10, figure A Noreen McMahon -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Gregg Fontes Sent: Thursday, October 23, 2008 10:44 AM To: [email protected] Subject: Fire Sprinkler Pipe through Mechanical Duct After review of NFPA 13, I cannot find a section that prohibits fire sprinkler pipe from passing through mechanical duct. Does anyone know of something in the Mechanical Code that would prohibit steel fire sprinkler pipe from passing through mechanical ductwork? Case in point, 2 1/2" fire sprinkler line passing through a +/-60" square duct. Mechanical contractor would seal the penetrations. Thanks, Gregg Fontes Cen-Cal Fire Systems, Inc. (209)334-9119 This email was scanned by D&G Technology Group Secure Scan and found to contain no virus or harmful content. Checked by AVG. Version: 7.5.549 / Virus Database: 270.8.2/1740 - Release Date: 10/22/2008 7:24 PM _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) CONFIDENTIAL AND PROPRIETARY: This email message is intended only for the use of the individual or entity to which it is addressed and may contain information that is privileged and confidential, nor is it, unless specifically stated, intended to be relied upon by any person or persons other than the individual or entity named above and no warranties or representations are made or intended to persons or entities not named above. If the reader is not the intended recipient, you are hereby notified that any dissemination, distribution or copying of this communication is strictly prohibited. If you have received this communication in error, please notify us immediately by telephone, return this message to the address above and delete all copies. Thank you. _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)