Dan, That is incorrect information. This is still a requirement in NFPA 13. Some had previously reported that FM was planning to remove it from the FM Data Sheet requirements. Someone was confused, as it has not, nor was it ever planned to be removed. In fact, as currently worded, the FM requirement could lead to including MORE than 2 additional heads in an ESFR remote area.
Jeff Hewitt, PE, SET, SFPE (Professional Member) Corporate Engineer Bi-State Fire Protection Corporation 241 Hughes Lane St. Charles, MO 63301 636-946-0011 636-946-5172 (FAX) -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of danarbel Sent: Tuesday, November 04, 2008 10:51 AM To: [email protected] Subject: RE: Fire Pump Suction Question regarding the number of ESFR heads required for hydraulic calc. The nominal number is 12. There was a requirement to add 2 heads if there are heads installed below beams or AC ducts. If I'm not wrong the addition of 2 heads was abolished. Please confirm or correct me, Dan Arbel _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)