Steve, 

As a design house how do you coordinate with designs of other disciplines if 
the project was issued by an AE firm? What do they typically give you to work 
with?

How precise are your dwgs. as far as dealing with obstructions and coordination?

What I had seen happening around here was the design houses were cranking out 
heads on a drawing,  that was their billing method, $/head designed, not 
spending a lot if any time on coordination, just developing a layout that could 
be submitted to the AHJ and EOR and the contractor could work out the "bugs" in 
the field.  The dwgs. were produced quickly but were becoming less and less 
useful.  This was not just from one company alone either.



Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com 


-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Steve Leyton
Sent: Wednesday, November 12, 2008 5:00 PM
To: [email protected]
Subject: RE: Ideal World - What info would you want from a PE

Generally, we offer #9, but often clients want more limited services and
have done some version of 2-8 on many projects.   You left out
performance specifications and that's a pretty important piece of the puzzle if 
you're not provided plans.

I first started writing spec's by accident in about 1989.   A local
architect issued "boilerplate" on a large Type 5 retail project.   Our
firm earned the bid, prepared plans, submitted to the FD and moved on.
We were at 20% when we got a memo from the GC instructing us to submit
to FM ...  uh-oh.   Turns out the spec's overlooked the owner's
insurance and it turned into a nightmare R&R of much of the installed
piping and an urgent re-design on everything.   After the dust settled I
approached the architect and instead of blowing me off, they were very 
interested in improving their documents and the short version is that I started 
writing performance spec's for them on the side.  Same firm gave PD&C its start 
in 1995 by hiring us to work on a very large project.

For the first 4 or 5 years, most of our projects were just "spec's and 
submittal review".  These days, we don't even do such limited scopes any more - 
most clients have tasted the benefits of a complete document set
and that's the preference.   My biggest concern starting out was that
local sprinkies - many of them former competitors - would resent "losing" the 
design work to a design only firm.  Ironically, I've heard over and over that 
having a "level playing field" and a solid set of spec's (project and 
technology-specific, not boilerplate) is a welcome asset.  We generally see 
more competitive bids, MUCH tighter bid scatter, fewer changes and ultimately, 
lower overall costs and
on-schedule deliveries.   The highest compliment I get is when a
contractor calls and says, "I see you wrote the spec' on the Such and
Such project ..."    I'm proud that even when there aren't plans, or if
our firm isn't identified on the project directory, that our work is 
recognizable and apart from the crap that unfortunately still makes up the 
majority of work product in this sector.  Unfortunately, we've had to send 
cease and desist letters a few times to architects and engineers who have 
borrowed our format.  

Nonetheless, a decent set of spec's can be of great value to bidders where 
there are no plans.  A document should include accurate hazard groups and 
design areas, commodities classifications and associated storage design 
criteria, selection of sprinklers, extended coverage and residential product 
technologies as applicable, backflow and UG stuff,
etc., etc.   Too often, we still see spec's with out of date insurance
references, incomplete or inaccurate codes and standards references,
non-existent or out-of-business manufacturers and all that.   

Steve Leyton
Protection Design & Consulting
San Diego, CA


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Steve Kowkabany
Sent: Wednesday, November 12, 2008 1:21 PM
To: [email protected]
Subject: Ideal World - What info would you want from a PE

Since we're on the topic of contract documents, what do the contractors out 
there want to see as an ideal level of detail from the PE on plans and specs?  
I'll throw out some examples based on what I have seen ranging from the minimum 
(which puts the entire design onus on the contractor) to the maximum 
(full-blown layout).

 

1)      No design docs - just "design per NFPA 13, 16, 20, 24, etc."

2)      Hazard classifications of all areas within the building
including
densities to be used, size of remote area, etc. - including design criteria for 
special situations like dry storage of boats, special hazards, and other 
storage scenarios

3)      System type specified - wet, dry, antifreeze, etc.

4)      Water supply totally worked out including a coordinated
underground
design, backflow preventer location and type, and recent flow test info

5)      Code references identified for sources of requirements from
local
building codes and fire codes

6)      Fire alarm system interface details

7)      Structural coordination details such as locations of mains or
standpipes will need to penetrate floors or firewalls

8)      Partial layout - such as the location of just mains, or just
heads,
or just some system components that are critical to the owner or architect

9)      Full blown layout and hydraulic calcs (similar to what white
paper
level of detail)

10)  Full blown layout plus stocklisting - contractor just fabricates 
components and assemblies and entire design responsibility is on the engineer

 

In an ideal world, where every engineer and contractor had NICET 4 knowledge 
and experience, what would be the ideal level of detail for you as contractors? 
 Does too much information restrict your ability to be creative and bid 
competitively, or would it be better to have completely engineered drawings to 
fabricate and install from.  I'd love to hear your thoughts.

 

Thanks,

 

 

Steve Kowkabany, P.E.

Fire Protection Engineer

Neptune Fire Protection Engineering LLC

616 Davis Street

Neptune Beach, FL 32266

904-652-4200 Phone

904-212-0868 Fax 

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
 

__________ Information from ESET NOD32 Antivirus, version of virus signature 
database 3607 (20081112) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__________ Information from ESET NOD32 Antivirus, version of virus signature 
database 3607 (20081112) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to