Besides the two rooms we are protecting (hazardous materials) the building does 
not require sprinklers and the owner does not want them.  In our opinion it is 
foolish not to, but not our call.

Reed A. Roisum, CET
Fire Protection Technician

Ulteig Engineers, Inc.
3350 38th Avenue South
Fargo, ND 58104-7079

Direct Number: 701.280.8580
Mobile: 701.212.8810
Main Office: 701.280.8500


-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED]
Sent: Monday, November 17, 2008 7:22 AM
To: [email protected]
Subject: RE: Sprinkler Main Protection

Just curious but why is the area the main is passing through unprotected?


Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com


-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Reed Roisum
Sent: Friday, November 14, 2008 6:08 PM
To: '[email protected]'
Subject: RE: Sprinkler Main Protection

No, the area the main passes through is not to be sprinklered, but it seems as 
though there was a reference that said if you are passing through an 
unsprinklered area you need to protect the pipe from fire by having uprights on 
the main.

Reed A. Roisum, CET
Fire Protection Technician

Ulteig Engineers, Inc.
3350 38th Avenue South
Fargo, ND 58104-7079

Direct Number: 701.280.8580
Mobile: 701.212.8810
Main Office: 701.280.8500


-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon
Sent: Friday, November 14, 2008 4:50 PM
To: [email protected]
Subject: RE: Sprinkler Main Protection

Reed:

Did I miss understand the question? Where you talking about protecting that 
area with sprinkler heads (SSP or SSU) attached directly to the main, to 
provide protection to the area the main passed thru?

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED]
Sent: Friday, November 14, 2008 3:44 PM
To: [email protected]
Subject: Re: Sprinkler Main Protection

13-8.16.4.3.1:".....protected from mechanical and fire damage."
Forest Wilson
Cherokee Fire


In a message dated 11/14/2008 5:03:09 P.M. Eastern Standard Time, [EMAIL 
PROTECTED] writes:

It seems  as though there is a reference in 13 to providing sprinklers on a 
main that is  routed through an area that is otherwise unsprinklered.  Is there 
such a  reference, and if so, where?

Thanks,

Reed A. Roisum, CET
Fire  Protection Technician

Ulteig Engineers, Inc.
3350 38th Avenue  South
Fargo, ND 58104-7079

Direct Number: 701.280.8580
Mobile:  701.212.8810
Main Office:  701.280.8500
_______________________________________________
Sprinklerforum  mailing  list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For  Technical Assistance, send an email to:  [EMAIL PROTECTED]

To Unsubscribe, send an email  to:[EMAIL PROTECTED]
(Put the word unsubscribe in  the subject field)

**************Get the Moviefone Toolbar. Showtimes, theaters, movie news & 
more!(http://pr.atwola.com/promoclk/100000075x1212774565x1200812037/aol?redi
r=htt
p://toolbar.aol.com/moviefone/download.html?ncid=emlcntusdown00000001)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to