Four or 1%, whichever is greater, of each type. That would be for each system unless you can convince the AHJ that since they are all of a type and age that one system is representative of the entire building or negotiate some other number between one and ten.
On Mon, Nov 17, 2008 at 2:36 PM, Dyce Geoffrey H. <[EMAIL PROTECTED]> wrote: > We have a situation where there are aprox. 10 warehouse systems with > sprinklers over 50 years old which include offices, racks, and ceiling > sprinklers. If each system has 500 +/- sprinklers and each sample requires 4 > sprinklers or 1%, whichever is greater, what would you call a representative > sample of this building? > Thanks in advance > > Geoffrey H. Dyce > Sales Manager > Contractor I, #87582700012007 > NICET IV > Industrial Fire & Safety Inc. > Ph: 727-573-1556 > Fx: 727-572-7266 > Cell: 727-644-8872 > > _______________________________________________ > Sprinklerforum mailing list > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > For Technical Assistance, send an email to: [EMAIL PROTECTED] > > To Unsubscribe, send an email to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > -- Ron Greenman at home.... _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)