Russell, Check out the commentary on 8.15.9 (2007 ed.). You can determine whether you are dealing with "high-density mobile shelving". But that is kind of what it sounds like. Note what you need to do if you don't have 18" clear.
Reed A. Roisum, CET Fire Protection Technician Ulteig Engineers, Inc. 3350 38th Avenue South Fargo, ND 58104-7079 Direct Number: 701.280.8580 Mobile: 701.212.8810 Main Office: 701.280.8500 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Russell Sent: Friday, November 21, 2008 8:08 AM To: AFSA Subject: Collapsing File Storage System I need input as to what type/arrangement sprinklers you would use over the top of accordion type filing cabinets like are used in offices, etc. that are on tracks and can be parted to create a single aisle between any two adjacent cabinets (as you can see I'm struggling to come up with a technical name). The tops of these cabinets are 10" below a drop-in tile ceiling. All pipe is above this ceiling and using pendent sprinklers. Thanks Russell Rewis Brown Automatic Sprinklers, Inc. 107C Hemlock Street Valdosta, Georgia 31601 229-244-8130 [EMAIL PROTECTED] _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)