You consider the sprinkler demand including hose streams by the required duration in minutes and compare to the required standpipe demand and size the tank for the greater of the two. Since high-rise buildings are nearly all light and ordinary hazards, the standpipes will be more demanding 99.85% of the time. My opinion only ... Steve L.
________________________________ From: [email protected] on behalf of Dave Sent: Thu 12/11/2008 10:35 AM To: [email protected] Subject: Hi Rise Secondary Source ... again Greetings all.. I know I brought up this general topic once before but bear with me on it again. IBC-2006 Section 903.3.5.2 is the requirement for secondary on-site water supply in high rise buildings. Presuming we have an eligible building it comes down to sizing the storage tank or vessel. Code says 30 minutes of sprinkler demand - no problem on that part. It gets muddy at 'including hose stream allowance' -- here's my dilemma. This is a high rise building and it also requires a standpipe to NFPA 14. Many times this means a combination riser for sprinkler and standpipe. Now NFPA 14 tells us that when designing such combinations we do not apply the hose stream allowances of NFPA 13 since 14 is the hose stream standard when it comes to a standpipe system - still with me ?? How do I use a hose stream allowance for tank sizing when Im told not to apply hose stream allowances in the overall design and in reality the FD will be hooking up 2 1/2" hoses to the hose valves and pulling +200 GPM for hoselines. Do we calculate the 250 GPM as the 'hose stream allowance'? If we use the 100 GPM hose stream in NFPA 13 in spite of all this then we will be flowing +200 and having only designed for 100 GPM we will no longer have the 30 minutes of sprinkler duration in a common riser system. What say everyone else - I'm totally up in the air and need something to go with. Dave P. AHJ in NJ _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) __________ Information from ESET NOD32 Antivirus, version of virus signature database 3684 (20081211) __________ The message was checked by ESET NOD32 Antivirus. http://www.eset.com <http://www.eset.com/>
_______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)