If you're supplying sprinklers in the electrical room you can pass through it.  
You don't run through the electrical room if you're not protecting it to 
service an adjacent room.

As far as service clearances, generally when you're at the ceiling, you are 
most likely outside of that "sacred" space.  

And sprinkler piping does get some preferential treatment (one of those rare 
occasions) in comparison to other utilities within electrical rooms.  


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of George Church
Sent: Tuesday, December 16, 2008 1:22 PM
To: [email protected]
Subject: RE: Electrical Rooms

I understood you can run into your head(s) but not back out to others.
Kind of an ENTER HERE followed by NO EXIT.

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brian Harris
Sent: Tuesday, December 16, 2008 11:42 AM
To: [email protected]
Subject: RE: Electrical Rooms

So this doesn't prohibit pipe from passing through an electrical room, right? 
You just need to stay out of the "dedicated" space? 


Brian Harris
FDFP INC.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Tuesday, December 16, 2008 10:47 AM
To: [email protected]
Subject: Re: Electrical Rooms

NEC Article 110.26(F)(1)(a).

Dedicated Electrical Space. The space equal to the width and depth of the 
equipment and extending from the floor to a height of 1.8 m (6 ft) above the 
equipment or to the structural ceiling, whichever is lower, shall be dedicated 
to the electrical installation. No piping, ducts, leak protection apparatus, or 
other equipment foreign to the electrical installation shall be located in this 
zone.

Thank You

Rahe Loftin, P.E.
Region 7 - GSA
Office - 817-978-7299
Fax - 817-978-8644
Cell - 817-371-3102



                                                                           
                                                                           
             "Brian Harris"                                                
             <br...@firstdefen                                          To 
             sefire.com>               [email protected]    
             Sent by:                                                   cc 
             sprinklerforum-bo                                             
             un...@firesprinkl                                     Subject 
             er.org                    Electrical Rooms                    
                                                                           
                                                                           
             12/16/2008 09:36                                              
             AM                                                            
                                                                           
                                                                           
             Please respond to                                             
             sprinklerfo...@fi                                             
              resprinkler.org                                              
                                                                           
                                                                           




I know it's in the code but I can't put my finger on it, what section talks 
about not running a sprinkler line through an electrical room? While I'm on it 
what section prohibits running through a stairwell? Thanks, I'm in a time 
crunch otherwise I wouldn't bother you........


Regards,


<http://www.firstdefensefire.com/>








E-mail message checked by Spyware Doctor (6.0.0.386) Database version:
5.11350 http://www.pctools.com/en/spyware-doctor-antivirus/
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)





E-mail message checked by Spyware Doctor (6.0.0.386) Database version:
5.11350 http://www.pctools.com/en/spyware-doctor-antivirus/





E-mail message checked by Spyware Doctor (6.0.0.386) Database version: 5.11350 
http://www.pctools.com/en/spyware-doctor-antivirus/
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to