That is what I had planned and put a air relief or vacuum break on the fill
pipe. One thing we were debating was the use of plastic or steel, but we
decided to groove it and go steel.

Thanks,

Bobby Gillett
Sr.Project Manager
Key Fire Protection, Inc.
[email protected]
(731) 424-0130 office
(731) 424-9285 fax
(731) 267-4853 cell

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Wednesday, January 07, 2009 8:25 AM
To: [email protected]
Subject: Re: 13R Tank/Pump Piping

Bobby, I'm not sure what there is for specific guidance. What I 
usually try to do is keep all of the suction pipe the same size (or 
larger, if distance is an issue) as the pump suction. I also like to 
valve each tank so if a problem develops, then you can isolate the 
tank and keep the system in service. The value of that has been 
debated on the Forum before, but I still prefer that arrangement. The 
pump or tank manufacturers might have something to say about it, too.



At 08:56 AM 1/7/2009, you wrote:
>We are installing a 13R system. There is a pump room with (5) 400gallon
>plastic tanks that will be piped together. Is there anything that gives
>direction for the requirements for piping materials, valves, etc. between
>the tanks and pump?
>
>
>
>Thank You,
>
>
>
>Bobby Gillett
>
>Sr.Project Manager
>
>Key Fire Protection, Inc.
>
>[email protected]
>
>(731) 424-0130 office
>
>(731) 424-9285 fax
>
>(731) 267-4853 cell
>
>
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG - http://www.avg.com 
Version: 8.0.176 / Virus Database: 270.10.3/1877 - Release Date: 1/5/2009
7:20 PM

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to