The lack of detail on the engineer's sprinkler drawings is often
dictated by the client, not the A/E firm.  For example, the Navy will
not allow us to do detailed designs because they (like many others)
believe that will lead to change orders.  Somehow they don't have a
problem with the HVAC engineer or the plumbing engineer showing their
detailed designs.  I would like to see equal treatment; the HVAC
engineers should show a hatch pattern on the floor plan with a note that
says "deign ductwork to provide a comfortable environment.". 

Paul Pinigis, P.E.
Life Safety Department Head



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Wednesday, January 07, 2009 10:57 AM
To: [email protected]
Subject: RE: another fire - this will be interesting

You'll have to do more than just make your magical FPE's appear from the
sky, you'll have to change the mindset of an entire industry. 

For too long the A/E industry has felt it was a waste of time and money
to do detailed design for fire protection, the thought being that since
the contractor did all that for free, why duplicate the effort.  Less
hours spent on fire protection meant more hours to be used by someone
else or could be saved altogether.  That makes the PM look good, hours
unspent=bigger bonus.

So even if you did have your super FPE's appear, they would still not be
able to produce the documents the contractors would love to see.

Trying to educate project managers, schedulers, department managers
etc...... is an uphill battle.  They don't understand the FP industry,
how it works, who does what, submittals to AHJ's, minimum information
required on a drawing package, when in the course of the project fire
protection needs to start and finish, what info is needed to do the fp
design work (when you are doing more than an "X" on a drawing, and the
list of obstacles goes on and on.  Next project, you start the battle
all over again.

Other disciplines don't understand the rules you have for head spacing,
deflector distances below decks, obstructions, water pressure and flow
issues, etc. Most think FP as being able to move where ever so they have
more room and are often told that very thing by their supervisors.

You don't know how many times I've been told by ME's who are supposed to
be responsible for FP work that it is so confusing.  What's scary is
most probably know just enough to pass the FPE.  So that's obviously not
the answer to the overall problem.




Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George
Church
Sent: Tuesday, January 06, 2009 11:24 AM
To: [email protected]
Subject: RE: another fire - this will be interesting

We'd need several hundred qualified FPEs (or equal) to fall out of the
sky in order to do what you  say, as desirable a concept as you present.
That and a couple thousand more so we contractors can put them on staff
so we can evaluate water supplies and perform hydraulic calculations in
accordance with the SFPE White Paper (unless the more recent revs have
allowed us to calc systems like we've been doing as an industry since
there were calcs).

Instead we have FPE-Plumbing Designer ACTING like FPEs despite being
only casually familiar with our industry, codes, standards, materials,
etc.- i.e., practicing outside their area of competence. 

And so we don't just call this PE bashing, I'll point out that
contractors evaluating water supplies- and that would be all of us
performing calcs based on some flow test, ours or someone elses- need to
be aware of lowest tank gradient, the importance of correcting for
elevation and other corrections needed to move the data correctly from
the test to the floor flange. I have a project where my competitor doing
an adjacent building on same site off same main is using a flow test
result that is 10 PSI higher than mine, with twice the flow. I've become
familiar with the site, water supply, and did a more accurate test than
they did, I guess that's the price of being able to sleep at night.

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Paul
Pinigis
Sent: Tuesday, January 06, 2009 10:35 AM
To: [email protected]
Subject: RE: another fire - this will be interesting

Very well said John.  This is exactly the approach that we take; we look
at the building or project holistically and our fire protection
engineers direct the architect, mechanical, electrical, structural,
telecom, etc. to ensure coordination and compliance.  

Paul Pinigis, P.E.
Life Safety Department Head

Hankins and Anderson
Consulting Engineers
4880 Sadler Road Suite 300
Glen Allen, VA 23060
v: (804) 285.4171 f: (804) 217.8520
d:(804) 521-7011

http://www.haengineers.com
 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of John
Drucker
Sent: Tuesday, January 06, 2009 9:46 AM
To: [email protected]
Subject: RE: another fire - this will be interesting


Simply put "fire protection" is not seamless. Often enough it's a
patchwork of pieces and parts assembled without a clear and common
objective. We see this everyday with smoke detectors being installed in
unsprinklered elevator hoistways because no one told the alarm engineer
that sprinklers had been eliminated by the sprinkler engineer, or fire
dampers installed in one hour walls in fully sprinklered buildings
because no one told the mechanical engineer. The disconnect with the
fire service is yet another example, site planning left to the civil
engineer without regard to fire protection needs.

What we need are MEPF firms, engineering firms that employ and fully
utilize fire protection engineers to look at the big picture, assess,
plan, design, coordinate and supervise cost effective and efficient fire
protection solutions. 

If as a fire protection engineer you're simply designing fire alarm or
sprinkler systems you are not working to your full potential !  There
are firms that provide life safety analysis to provide passive fire
protection solutions, often coined working for the "dark side" they
nonetheless do what others are not, looking at the big picture. High
rise sprinklers in Chicago or San Diego anyone ? 

So how does the active fire protection community counter this claim,
perhaps by long term planning, synergistic value driven engineering. It
goes all the way back to codes and standards, how many cycles did it
take to recognize sprinklers in fully sprinklered buildings for
notification survivability on fire alarm systems ?

One stop shopping ladies and gentlemen, one stop shopping.

Sincerely

John Drucker
Fire Protection Subcode Official (AHJ)
Building/Fire/Electrical Inspector

Safe Buildings Save Lives !



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Chris
Cahill
Sent: Monday, January 05, 2009 10:36 AM
To: [email protected]
Subject: RE: another fire - this will be interesting

Ron said "(I suspect the savings in mains, hydrants, fire stations,
apparatus and firefighters is way more than a wash in fully sprinklered,
planned communities than the cost of sprinklering schools)."

Were these savings realized?  Last I read which was a long time ago
there was very little saved on the reduction in the list you provided.
They never actually followed through in reducing mains and limiting
stations etc.  I will certainly say in the macro scale these saving are
not being fully realized.  Hell we still have fully paid stations in
many departments that average < 1 call a day and plenty more that are <
2.  As a pay-per-call volunteer I saw more fire than many paid guys in
these parts.  

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ron
Greenman
Sent: Friday, January 02, 2009 2:05 PM
To: [email protected]
Subject: Re: another fire - this will be interesting

Good point so far overlooked. There's also the dubious "saved
foundation" success that may have not been worth the risk of going into
harm's way. And no one has brought up the environmental advantages of
sprinklers--less smoke, less destroyed building materials to dispose of,
less dirty water to process and, of course, less water used overall. And
the Scottsdale less public money spent on firefighting infrastructure (I
suspect the savings in mains, hydrants, fire stations, apparatus and
firefighters is way more than a wash in fully sprinklered, planned
communities than the cost of sprinklering schools).

On Fri, Jan 2, 2009 at 11:49 AM, Dave <[email protected]> wrote:
> Since we are offering up various thoughts and theories on the general
application of sprinklers .....  Regardless of how much egress time is
allegedly available or occupant ability to respond or even construction
materials & methods - there still is a fire in a building -  Presuming
we get everyone out safely and that eliminates the 'life safety need for
sprinklers' will we then NOT call the fire department to respond??
>
> Once there's a fire in a building there is another completely real 
> life
hazard in play - the responding emergency personnel.  Some may enter the
building and be very close to harm's way and others may respond and have
ancillary functions - traffic control, EMS, crowds etc.  Regardless of
the specifics we can generally agree that a fire in a non-sprinklered
building will be larger than the same fire in a sprinklered building.
It's not always the fire but medical emergencies or trips & falls that
create the threat of harm.  The larger the fire the greater its duration
and intensity
- all of which increase exposure and life safety risk to responders.
>
> Personally I don't get behind the non-combustible and limited or low 
> fuel
load argument as a valid application of sprinkler omission.  Maybe thats
just my narrow focus or perhaps its because I've been to alot bigger
fires in non-sprinklered buildings than sprinklered buildings.  The
closer you get to the gun - the bigger the bullet.
>
> Thanks & Happy New Year
> Dave P.
> Fireman first and always.
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: 
> [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>



--
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or
entity to which it is addressed and may contain information that is
privileged and confidential, nor is it, unless specifically stated,
intended to be relied upon by any person or persons other than the
individual or entity named above and no warranties or representations
are made or intended to persons or entities not named above.  If the
reader is not the intended recipient, you are hereby notified that any
dissemination, distribution or copying of this communication is strictly
prohibited.  If you have received this communication in error, please
notify us immediately by telephone, return this message to the address
above and delete all copies.  Thank you.

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to