NFPA-13 2007 says calc 5 sprinklers in the corridor with protected openings (11.2.3.3.6) and 5 sprinklers in the corridor with unprotected openings (11.2.3.3.7). Previous editions required 7 sprinklers with unprotected openings. The explanatory text for 11.2.3.3.6 in the handbook still mentions 7 sprinklers. Anyone know what the deal is with this? Thank you.
Mark Hasenmyer, PE MEH Fire Protection Engineering LLC 1311 River Oaks Drive Flower Mound, TX 75028 Office (972) 874-2662 Fax (972) 874-5591 _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)