NFPA-13 2007 says calc 5 sprinklers in the corridor with protected openings
(11.2.3.3.6) and 5 sprinklers in the corridor with unprotected openings
(11.2.3.3.7).  Previous editions required 7 sprinklers with unprotected
openings.  The explanatory text for 11.2.3.3.6 in the handbook still
mentions 7 sprinklers.  Anyone know what the deal is with this?  Thank you.

 