IFC 903.3.1.1.1 #4 would appear to agree with 8.14.1.2.2.  If you have no 
combustibles above the ceiling then what's his issue? 

Typically the "room" or "area" listed in 903.1.1 is deemed as being a 
potentially occupied space.  If you read 315.2.4 only those spaces which are 
used for storage require fire resistant rated construction or sprinklers.  So 
it would seem obvious that if the space were not used for storage it would not 
be subject to those requirements.

His interpretation of 903.3.1.1 contradicts 903.3.1.1.1.   There are obviously 
conditions where not spinklering an area is allowed with certain exceptions.

As indicated in the body of the Fire Code, NFPA 13 is a referenced standard 
essentially making it a part of the Code, the installation rules of NFPA 13 
apply. 



Here is some wording out of the IFC 2006 Commentary relating to 903.3.1.1:
--------------------------------------------------------------------------
The extent of coverage and distribution of sprinklers is based on the NFPA 13 
standard. Numerous conditions exist in the standard where sprinklers are 
specifically required and also where they may or may not be located. Once it is 
determined that the sprinkler system is to be in accordance with NFPA 13, that 
standard must be reviewed for installation details. For example, exterior 
spaces such as combustible canopies are required to be equipped with sprinklers 
according to Section 8.14.7 of NFPA 13 where the canopy extends for a distance 
of 4 feet (1219 mm) or more. A 3-foot (914 mm) combustible canopy would not 
require sprinklers and neither would a 6-foot (1829 mm) canopy constructed of 
noncombustible materials, provided there is no combustible storage under the 
canopy.  Exceptions for the use of NFPA 13R and 130 systems are addressed 
throughout the code when exceptions based upon the use of sprinklers are 
provided. More specifically, if the use of these other standards is 
appropriate, it will be noted within the exception. For a building to be 
considered "equipped throughout" with an NFPA 13 sprinkler system, complete 
protection must be provided in accordance with the referenced standard, subject 
to the exempt locations indicated in section 903.3.1.1.1.


Concerning 903.3.1.1.1:
--------------------------------------------------------------------------------
This section allows the omission of sprinkler protection in certain locations 
if an approved automatic fire detection system is installed. Buildings in 
compliance with one of the four listed conditions would still be considered 
fully sprinklered throughout in compliance with the code and NFPA 13 and thus 
are eligible for all applicable code alternatives, exceptions or reductions. 
Elimination of the sprinkler system in a sensitive area is subject to the 
approval of the fire code official.

Condition 4 requires the construction of the room or area, as well as the 
contents, to be noncombustible.
An example would be an area in an unprotected steel frame building (Type liB 
construction) used for steel or concrete block storage. Neither involves any 
significant combustible packaging or sources of ignition, and few combustibles 
are present (see Figure 903.3.1).
Because installation is required to be in accordance with NFPA13, if the 
standard allows for the omission of sprinklers in any location, then the 
building is still considered as sprinklered throughout. For example, Section 
8.14.8.1.1 of NFPA 13 allows sprinklers to be omitted from bathrooms in certain 
circumstances. If sprinklers are not provided in the bathrooms due to the 
conditions stipulated in NFPA 13, the building would still be considered as 
sprinklered throughout in accordance with NFPA 13 and the IBC.


Good luck, hopefully you're not dealing with one of those guys whose mantra is 
"My mind's made up, don't confuse me with facts."


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Chris Russel
Sent: Thursday, February 05, 2009 12:21 PM
To: [email protected]
Subject: IFC vs NFPA 13 issue

Hello,

I have a disagreement with the fire marshal and I would like another opinion. I 
have a prefabed metal building framed with sheet metal studs in all areas but 
the elevator shaft which is a 2 hour fire wall made of wood and sheetrock. 

 

We omitted sprinklers in the area above the t-bar lid per NFPA 13/2002
8.14.1.2.1 because this area is of noncombustible construction and limited 
combustible construction.

 

The fire marshal has stated that limited combustible construction is not 
allowed per the IFC per the following code. 

IFC section 903.3.1.1 - NFPA 13 sprinkler systems.

Where the provisions of this code require that a building or portion of thereof 
be equipped throughout with an automatic sprinkler system in a accordance with 
section 903.3.1.1, sprinklers shall be installed throughout in accordance with 
NFPA 13 except as provided in Section 903.3.1.1.1.

903.3.1.1.1 - Exempt locations

Automatic sprinklers shall not be required in the following rooms or areas 
where such rooms or areas are protected with an approved automatic fire 
detection system in accordance with section 907.2 that will respond to visible 
or invisible particles of combustion. Sprinklers shall not be omitted from any 
room merely because it is damp, of fire-resistance rated construction or 
contains electrical equipment. #4 In rooms or areas that are of noncombustible 
construction with wholly noncombustible contents.

 

It is my opinion that 903.3.1.1.1 addresses areas exempt from 903.3.1.1 i.e.
exceptions to the requirement of an NFPA 13 system. This does not mean that 
areas exempt from coverage in NFPA 13 must conform to IFC 903.3.1.1.1. 

 

Thanks,

 

Chris Russell



t. 360.734.4940
f. 360.647.9540

securitysolutionsnw.com 

 

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to