Scot,

IBC 102.4 & IFC 102.6  Reference Codes and Standards

"The codes and standards referenced in this code shall be considered part of 
the requirements of this code to the prescribed extent of each such reference. 
Where differences occur between provisions of this code and referenced codes or 
standards, the provisions of this code shall apply".

As such the IBC and/or IFC trumps the reference standards incorporated therein.

Furthermore only those sections or a standard specifically referenced 
(prescribed) by the IBC/IFC apply. If we look closely at  Chapter 35 (IBC) and 
Chapter 45 (IFC) you will see that the far right column provides the prescribed 
reference to the IBC/IFC code section.  Both Chapter 35 and Chapter 45 
(Reference Standards) states; "The application of referenced standards shall be 
as specified in Section 102.4 (IBC) and 102.6 (IFC)

Hope that helps

John Drucker
Fire Protection Subcode Official
Building/Fire/Electrical Inspector
Red Bank, NJ

 

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of å... ....
Sent: Thursday, February 05, 2009 3:52 PM
To: [email protected]
Subject: Code vs Standard - expanded --IFC vs NFPA 13 issue

this seque will not help Chris
per se,
but which
text gets the trump play?

if contradiction exists
between Code and standard texts
(unlike the original questioned
  here, where we are in a
  grey area)
which verse is on first?


scot deal
excelsior fire engineering




On Fri, Feb 6, 2009 at 12:08 AM, <[email protected]> wrote:

> IFC 903.3.1.1.1 #4 would appear to agree with 8.14.1.2.2.  If you have 
> no combustibles above the ceiling then what's his issue?
>
> Typically the "room" or "area" listed in 903.1.1 is deemed as being a 
> potentially occupied space.  If you read 315.2.4 only those spaces 
> which are used for storage require fire resistant rated construction or 
> sprinklers.
>  So it would seem obvious that if the space were not used for storage 
> it would not be subject to those requirements.
>
> His interpretation of 903.3.1.1 contradicts 903.3.1.1.1.   There are
> obviously conditions where not spinklering an area is allowed with 
> certain exceptions.
>
> As indicated in the body of the Fire Code, NFPA 13 is a referenced 
> standard essentially making it a part of the Code, the installation 
> rules of NFPA 13 apply.
>
>
>
> Here is some wording out of the IFC 2006 Commentary relating to 903.3.1.1:
> ----------------------------------------------------------------------
> ---- The extent of coverage and distribution of sprinklers is based on 
> the NFPA
> 13 standard. Numerous conditions exist in the standard where 
> sprinklers are specifically required and also where they may or may 
> not be located. Once it is determined that the sprinkler system is to 
> be in accordance with NFPA 13, that standard must be reviewed for 
> installation details. For example, exterior spaces such as combustible 
> canopies are required to be equipped with sprinklers according to 
> Section 8.14.7 of NFPA 13 where the canopy extends for a distance of 4 
> feet (1219 mm) or more. A 3-foot (914 mm) combustible canopy would not 
> require sprinklers and neither would a 6-foot
> (1829 mm) canopy constructed of noncombustible materials, provided 
> there is no combustible storage under the canopy.  Exceptions for the 
> use of NFPA 13R and 130 systems are addressed throughout the code when 
> exceptions based upon the use of sprinklers are provided. More 
> specifically, if the use of these other standards is appropriate, it 
> will be noted within the exception. For a building to be considered 
> "equipped throughout" with an NFPA 13 sprinkler system, complete 
> protection must be provided in accordance with the referenced 
> standard, subject to the exempt locations indicated in section 903.3.1.1.1.
>
>
> Concerning 903.3.1.1.1:
>
> ----------------------------------------------------------------------
> ---------- This section allows the omission of sprinkler protection in 
> certain locations if an approved automatic fire detection system is 
> installed.
> Buildings in compliance with one of the four listed conditions would 
> still be considered fully sprinklered throughout in compliance with 
> the code and NFPA 13 and thus are eligible for all applicable code 
> alternatives, exceptions or reductions. Elimination of the sprinkler 
> system in a sensitive area is subject to the approval of the fire code 
> official.
>
> Condition 4 requires the construction of the room or area, as well as 
> the contents, to be noncombustible.
> An example would be an area in an unprotected steel frame building 
> (Type liB construction) used for steel or concrete block storage. 
> Neither involves any significant combustible packaging or sources of 
> ignition, and few combustibles are present (see Figure 903.3.1).
> Because installation is required to be in accordance with NFPA13, if 
> the standard allows for the omission of sprinklers in any location, 
> then the building is still considered as sprinklered throughout. For 
> example, Section
> 8.14.8.1.1 of NFPA 13 allows sprinklers to be omitted from bathrooms 
> in certain circumstances. If sprinklers are not provided in the 
> bathrooms due to the conditions stipulated in NFPA 13, the building 
> would still be considered as sprinklered throughout in accordance with NFPA 
> 13 and the IBC.
>
>
> Good luck, hopefully you're not dealing with one of those guys whose 
> mantra is "My mind's made up, don't confuse me with facts."
>
>
> Craig L. Prahl, CET
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491 Direct - 864.599.4102 Fax - 
> 864.599.8439 [email protected] http://www.ch2m.com
>
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Chris Russel
> Sent: Thursday, February 05, 2009 12:21 PM
> To: [email protected]
>  Subject: IFC vs NFPA 13 issue
>
> Hello,
>
> I have a disagreement with the fire marshal and I would like another 
> opinion. I have a prefabed metal building framed with sheet metal 
> studs in all areas but the elevator shaft which is a 2 hour fire wall 
> made of wood and sheetrock.
>
>
>
> We omitted sprinklers in the area above the t-bar lid per NFPA 13/2002
> 8.14.1.2.1 because this area is of noncombustible construction and 
> limited combustible construction.
>
>
>
> The fire marshal has stated that limited combustible construction is 
> not allowed per the IFC per the following code.
>
> IFC section 903.3.1.1 - NFPA 13 sprinkler systems.
>
> Where the provisions of this code require that a building or portion 
> of thereof be equipped throughout with an automatic sprinkler system 
> in a accordance with section 903.3.1.1, sprinklers shall be installed 
> throughout in accordance with NFPA 13 except as provided in Section 
> 903.3.1.1.1.
>
> 903.3.1.1.1 - Exempt locations
>
> Automatic sprinklers shall not be required in the following rooms or 
> areas where such rooms or areas are protected with an approved 
> automatic fire detection system in accordance with section 907.2 that 
> will respond to visible or invisible particles of combustion. 
> Sprinklers shall not be omitted from any room merely because it is 
> damp, of fire-resistance rated construction or contains electrical 
> equipment. #4 In rooms or areas that are of noncombustible construction with 
> wholly noncombustible contents.
>
>
>
> It is my opinion that 903.3.1.1.1 addresses areas exempt from 
> 903.3.1.1 i.e.
> exceptions to the requirement of an NFPA 13 system. This does not mean 
> that areas exempt from coverage in NFPA 13 must conform to IFC 903.3.1.1.1.
>
>
>
> Thanks,
>
>
>
> Chris Russell
>
>
>
> t. 360.734.4940
> f. 360.647.9540
>
> securitysolutionsnw.com
>
>
>
>  _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: 
> [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%3ASprinklerforum-reques
> [email protected]> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or entity to 
which it is addressed and may contain information that is privileged and 
confidential, nor is it, unless specifically stated, intended to be relied upon 
by any person or persons other than the individual or entity named above and no 
warranties or representations are made or intended to persons or entities not 
named above.  If the reader is not the intended recipient, you are hereby 
notified that any dissemination, distribution or copying of this communication 
is strictly prohibited.  If you have received this communication in error, 
please notify us immediately by telephone, return this message to the address 
above and delete all copies.  Thank you.

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to