As an Engineer, I inform them in writing
At 10:54 PM 2/6/2009, you wrote:
We are renovating a grocery store. The original install was 1989 and
the sprinkler pipe hangers are not proper (ie.1x 5-0 trapeze hangers
supporting 3" pipe, hangers attached to bottom chord of trusses,
etc.). Existing heads in areas not subject to remodel are corroded.
The specs are typical garbage applicable to a new install from 10 years ago.
I intend to notify the GC of the deficiencies formally.
How do some of you other contractors address this?
Forest Wilson
Cherokee Fire
Sent from my Verizon Wireless BlackBerry
-----Original Message-----
From: "A.P.Silva" <[email protected]>
Date: Fri, 6 Feb 2009 20:06:31
To: <[email protected]>
Subject: RE: CEILING CLOUDS - AGAIN
I agree. Not both sets concurrently. The origina post seemed to say
deflectors below the clouds were 12" below the roof deck. Also it said
clouds were 12" below the roof deck. Won't that make the deflectors more
than 12" below the deck, unless of course, concealers were used? If the
deflectors were 12" or less below the roof deck, I would provide heads below
the clouds only.
Tony
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve Leyton
Sent: February 6, 2009 5:53 PM
To: [email protected]
Subject: RE: CEILING CLOUDS - AGAIN
If the standard specifies that we don't have to calculate both complements
when the obstruction is as narrow as 4'-1", I have a hard time imagining
what would be the basis for a concurrent calculation where the obstruction
is (generally) much larger. There's going to be a lot more heat moving past
sprinklers below narrower obstructions than if they were installed on a 20'
or 30 or wider cloud. I agree with your premise entirely, that flexible
joints or unique conditions below the clouds could make them more demanding
- that's what I said too. And yes, perhaps some will operate above and some
below, based on leakage of byproduct and heat through and around clouds to
the deck above, not to the extent that you have concurrent operation of two
full design areas.
Why would we put them under anything over 4' wide and not calc' those
concurrently too?
Now I would go the extra mile and say no reduction of the design area for
QR, just to be on the safe side ...
Steve Leyton
Protection Design & Consulting
San Diego, CA
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Friday, February 06, 2009 4:29 PM
To: [email protected]
Subject: RE: CEILING CLOUDS - AGAIN
Steve,
I'm not sure I agree. Aside from what the book says, I look at this type of
situation and I have a couple issues with it. Sprinklers at the deck are
typically uprights directly off a branch line (or perhaps a short sprig).
The pendent sprinklers may be fed by swing joints or flexible drops, which
could make those sprinklers more hydraulically demanding. This could make
the area below the clouds the most hydraulically demanding. However, I can't
say if the ceiling jets on a cloud would be sufficient to activate
sprinklers below them without the possibly activating sprinkler above.
Without fire tests or other research to verify different, I would assume
that some combination of sprinklers at the deck and below the cloud would
operate. Since we are charged by NFPA 13 with calculating the most
hydraulically remote area, my conclusion is that both levels would have to
be calculated to conservatively predict what would actually happen.
Typically, sprinklers below obstructions over 4 ft tend to be relatively
widely spaced and be relatively small compared to the ceiling area. This may
not necessarily hold true for ceiling clouds, especially given the
arrangements I have seen. The dynamics of the clouds could be very different
than that of a few sections of ductwork.
We need some research and testing and hopefully it will happen before a
significant fire loss.
Todd
At 06:51 PM 2/6/2009, you wrote:
>Do not concur. If the cloud condition is such that your best judgment
>is to provide a complete complement of sprinklers above, then you would
>calculate either above or below the clouds, as we always have for
>obstructions like ducts and in accordance with the exception spelled
out
>in 22.4.4.6.3 (2007 ed.). We often use SSP's above clouds and EC's
>below, especially when existing sprinklered buildings are being
>re-modeled or there's tenant turnover in an office shell, so sometimes
>it's two separate calc' areas but not a concurrent calculation of two
>different complements of sprinklers.
>
>
>Steve Leyton
>Protection Design & Consulting
>San Diego, CA
>
>
>
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of
>[email protected]
>Sent: Friday, February 06, 2009 2:21 PM
>To: [email protected]
>Subject: Re: CEILING CLOUDS - AGAIN
>
>And calculate both levels of sprinklers. You have no idea what is
really
>going to happen on a fire.
>
>
>Sent from my Verizon Wireless BlackBerry
>
>-----Original Message-----
>From: "Jeff Hewitt" <[email protected]>
>
>Date: Fri, 6 Feb 2009 16:07:37
>To: <[email protected]>
>Subject: RE: CEILING CLOUDS - AGAIN
>
>
>Travis,
>
>Since we have no specific guidance on this topic, my recommendation is
>that you must protect to deck first, and deal with the obstructions
>second.
>
>With this criteria, I would recommend both above and below the clouds.
>
>Just my thoughts
>
>Jeff Hewitt, PE, SET, SFPE (Professional Member) Corporate Engineer
>241 Hughes Lane
>St. Charles, MO 63301
>
>636-946-0011
>636-946-5172 (fax)
>314-574-6989 (cell)
>
>Fire Sprinklers Save lives.
>Can You Live Without Them?
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Travis
>Mack, SET
>Sent: Friday, February 06, 2009 3:50 PM
>To: [email protected]
>Subject: CEILING CLOUDS - AGAIN
>
>I have a project with lots of floating clouds. The clouds slope with
>the roof deck and are 1' below the roof deck. If I place a sprinkler
>in
the
>cloud, is one req'd in the space above the cloud? I would normally put
>sprinklers above the clouds, but with the deflector already at 12"
below
>the
>roof deck based on the cloud height, do you really need the sprinklers
>above the clouds?
>
>Please feel free to call if you have any questions or comments.
>
>Travis Mack, SET
> <mailto:[email protected]>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to:
>[email protected]
>
>To Unsubscribe, send an email
>to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to:
>[email protected]
>
>To Unsubscribe, send an email
>to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>
>__________ Information from ESET NOD32 Antivirus, version of virus
>signature database 3834 (20090206) __________
>
>The message was checked by ESET NOD32 Antivirus.
>
>http://www.eset.com
>
>
>
>__________ Information from ESET NOD32 Antivirus, version of virus
>signature database 3835 (20090206) __________
>
>The message was checked by ESET NOD32 Antivirus.
>
>http://www.eset.com
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to:
[email protected]
>
>To Unsubscribe, send an email
to:[email protected]
>(Put the word unsubscribe in the subject field)
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]
To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
__________ Information from ESET NOD32 Antivirus, version of virus signature
database 3835 (20090206) __________
The message was checked by ESET NOD32 Antivirus.
http://www.eset.com
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]
To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]
To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]
To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]
To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)