You are correct on many fronts.

There is an additional coef for flowing a large orifice (4", etc).

Most AHJ's don't apply it.  

Most contractors don't apply it.

It probably doesn't make a difference on LH and OH.  But here in the land of
50 psi water it can.   

And to Thom's point any other type of orifice negates this extra coef.  FYI
I've never heard of using hose monster for this purpose other than previous
reference on the forum. 


Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Travis Mack,
SET
Sent: Thursday, February 12, 2009 11:09 AM
To: [email protected]
Subject: flow tests using pumper connections

How many of my colleagues out there apply the requirements of NFPA 291 when
calculating the flow tests done with a pumper connection, instead of the 2½"
outlet?  I was taught that when using the 4", 4½" or 5", whatever your
hydrant is, you have to add another coefficient.
 
Reference is
4.8.2  For pumper outlets, the approximate discharge can be computed from
Equation 4.7.3 using the pitot pressure (velocity head) at the center of the
stream and multiplying the result by one of the coefficients in Table 4.8.2,
depending upon the pitot pressure (velocity head).
 
(I can't paste the table and get it to format properly)
 
4.8.3   These coefficients are applied in addition to the coefficient in
Equation 4.7.3 and are for average-type hydrants.
 
4.7.3 is the standard equation: Q=29.83*c*d^2*p^.5
 
I have received a lot more flow tests from local water and fire departments
where this modification is not being used.  The funny thing is that when I
try to use this modification, the authority does not want to accept my
calculations because my flow is not what was provided.  I have just been
doing the calcs with the proper flows initially to get my sizes, then I just
put in the flow test provided and show a bigger safety margin.
 
This really only comes into play on large demand systems, such as storage.
It is not an issue on most LH and OH systems.
 
Have I been wrong all of these years, or are the local authorities I am
dealing with not up to date on the calculation method?
 
Travis
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]