We used to use this super pressure method a lot here also but it seems
to have fallen out of favor.

On Sun, Mar 1, 2009 at 3:08 PM, Chris Mak <[email protected]> wrote:
> You are right George.
>
> We seem to have very lille problem here in NZ with internal corrosion. 
> Oibviously, some does happen, but not on a frequent basis.
>
> We believe one of the reasons is that we do not a requirement for inspectors 
> test connections at all, and thus minimise the introduction iof oxygenated 
> water into our systems.
>
> Most of our systems are based on super-pressurising the system, with the 
> alarm signal generated by a drop in pressure. We need air trapped in the 
> system, to ensure that the pressure gauges don't operate like a temperature 
> gauge. The trapped oxygen seems to combine with the iron very quickly to form 
> the black iron oxide- can't remember my chemistry I ferrous or ferric oxide.
>
> I have seen pipe removed after 50 years of service which is as good as new. 
> With leaky systems, where fresh water is being introduced, I have seen pin 
> hole corrosion develop, under the typical turbacles, at the air water 
> interface.
>
> Regards
>
>
> Chris Mak
> Aon Sprinkler Certification
> Via Blackberry
>
>
> ----- Original Message -----
> From: "George Church" [[email protected]]
> Sent: 01/03/2009 05:58 PM EST
> To: <[email protected]>
> Subject: RE: statistics
>
>
>
> Well, if you want to meet someone with influence and pull with the
> development of NFPA #13, simply grab a copy of it and turn to the last page,
> and look in the mirror. You'll find a FORM FOR PROPOSALS ON NFPA TECHNICAL
> COMMITTEE DOCUMENTS that enables you to influence the development of NFPA
> #13.
>
> You may wish to introduce the requirement for air bleed-offs at high points,
> because otherwise you'll need to introduce a requirement for ITCs to be
> piped off the highest point and in many cases, that's the ridge far away
> from the exterior wall you'll want it piped to. I think separating the two
> items- air blled-off and ITC- will also enable you to not be stopped by
> those who like the ITC at the riser for convenience, economy, because their
> riser manifold design has it there, whatever. While you may use it as an air
> bleed-off, the ITC's function IS to test the alarm device. Hence the
> suggestion to enable two items to address two different tasks.
>
> I'm not a metallurgist, nor would many watch one on TV, so I won't address
> the claims you've made. I believe there was discussion many moons ago on the
> Forum WRT the NZ lack of MIC versus USA experience, and the difference in
> ITC Location was offered up as a possible reason.
>
> I understand PRVs will be required on all wet systems shortly, so one of the
> problems is already being addressed; if those were gridded systems, as I'd
> expect in a >1M SF facility, then the code already addressed the problem of
> high pressure and you applied it- PRVs.
>
> Rather than list all reasons in one proposal, I'd suggest breaking it into
> twain and providing technical substantiation for each.
>
> Congrats on going public with your complaints about ITCs, and I encourage
> you to take the next step so your thoughts will be considered by the
> committee.
> glc
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Rodney Hamm
> Sent: Sunday, March 01, 2009 5:38 PM
> To: [email protected]
> Subject: RE: statistics
>
> If anyone has any pull or influence with the development of NFPA 13........
>
> Please discuss the idiotic approach of installing Inspector's Test
> Connections at the sprinkler riser (~12 in. downstream of the flow switch).
> This has been considered "acceptable" by NFPA 13 since 2002 and is quickly
> becoming standard practice in the great state of Georgia. There are several
> significant reasons why this is a bad idea AND from an engineering
> standpoint this is a very poor design. The inevitable trapped air in the
> system causes or can potentially cause a number of problems: Excessive
> system pressure when temperatures increase, false water flow alarms due to
> air pocket expansion/contraction, failed water flow alarms due to cycling
> flow switches, increased rust on the interior surfaces of sprinkler piping,
> etc.
>
> >From what I have seen, most contractors or sprinkler designers who
> primarily
> install or design new systems have no idea this approach causes problems for
> the building owner and/or fire protection system inspectors. I can confirm
> these are common problems at several of the facilities I have visited over
> the past few years. In many instances, the only effective solution is to
> install a suitably located Inspector's Test Connection or bleed the air
> pockets using sprinklers at the highest elevations. We have installed air
> bleed off connections for numerous systems simply to allow trapped air to be
> removed from the high point. The problem is access at some facilities after
> the solid ceilings or other obstructions have been introduced.
>
> In my humble opinion, Inspector's Test Connections should be installed at
> the most remote point of each system. The connection point (prior to being
> piped to within 6 ft. of the floor level) should be at the highest elevation
> of the sprinkler system piping whenever possible. Auxiliary drains or low
> point drains should NOT be considered Inspector's Test Connections.
>
> I would assume it is safe to say anyone who has enough experience and
> personal dealings with inspections and/or problem solving (after the design
> phase and initial installation project has been completed) realizes that the
> Inspector's Test Connection serves more purposes than just testing the water
> flow alarms. {I have heard "the sole purpose of the ITC is to test the alarm
> device" so many times that I get a smile every time someone spouts it.} I
> simply disagree with the relatively recent change in NFPA 13 which allows
> this approach. I strongly believe the practice of installing the Inspector's
> Test Connection a few feet downstream of the water flow switch should be
> considered unacceptable.
>
> In many instances, the fire alarm companies and building owners have to deal
> with the issues caused by this poor design. They rarely if ever realize the
> true source or reason for the intermittent false alarms. They simple bypass
> the alarm or set the delays so high that flow switch cycling becomes a
> problem during alarm testing.
>
> We see systems with >175 psi on a regular basis caused by this
> problem.......some systems even peg the 300 psi gauges. On of my customers
> had 5 separate incidents where sprinklers developed leaks and/or popped open
> due to excess system pressure during Spring & early Summer of 2007. We added
> pressure relief valves in August of 2007 for all of their wet systems and
> this resolved the problem. This is a >1 million sq. ft. facility with
> several wet systems. False fire alarms and excess air pressure are very
> common problems when the ITC is not located at the most remote and/or
> highest elevation of the system piping. I could provide many more examples,
> but I think I have made my point.
>
> Black steel, moisture and trapped air allows more rust to develop on the
> interior surfaces of the sprinkler piping than if the majority of the
> sprinkler piping is full of water. Therefore, it would be safe to conclude
> that trapped air in the sprinkler systems will shorten the life of the
> sprinkler system piping.
>
> The fact that someone or some group convinced the NFPA committee to change
> the standard and the fact that the approach saves time and money during
> installation does not make it a good engineering design!
>
> There are probably a few instances where placing the ITC a few feet
> downstream of the flow switch should be considered acceptable due to limited
> or no feasible alternatives; however, these instances should be the last
> resort alternative rather than standard practice.
>
> Just one man's perspective!! I wonder if anyone on this forum agrees with me
> on this subject.
>
> Rodney K. Hamm, P.E.
> President/Owner
> Falcon Fire Protection
> Office  (478) 953-1677
> Cell  (478) 396-6988
> ------------------------------
>
> Date: Sun, 1 Mar 2009 11:53:24 -0500
> From: Mike Cabral <[email protected]>
> Subject: RE: statistics
> To: [email protected]
> Message-ID: <20090301115324.sekkv.1683217.r...@mp20>
> Content-Type: text/plain; charset=utf-8
>
> A long time ago when I was a young man I did a lot of work on old systems in
> industrial buildings in New England. . . old textile mills mostly. I wish I
> had a few $ for every piece of 3/4" pipe I changed to 1" on these old pipe
> schedule systems.
>
> A high vent was almost always present with instructions on filling the
> system posted on the riser. The location of the vent or vents was stated and
> the order or the procedure for operating them was often posted. Some times
> the instructions would advise you to open the vent while filling other times
> the vent was opened after the system was under pressure.
>
> If you followed the instructions you went home for the day and that was
> that. If you didn't you could expect a call sometime through the night
> because water would move as the air migrated through the system and trip the
> alarm.
>
> These systems were old in the late 1960's and early 1970's. . . willing to
> bet most of them are still in service. Venting the air keeps trapped air out
> of the mains and cross mains which would eliminate the air water interface
> which if present invites corrosion.
>
> Sometimes there is something to learn from accent history
>
> Mike Cabral
>
> ---- George Church <[email protected]> wrote:
>> Minimize false trips and air for MIC.
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Forest
> Wilson
>> Sent: Sunday, March 01, 2009 10:43 AM
>> To: [email protected]
>> Subject: Re: statistics
>>
>> What advantage is there to venting the air? Other than response time?
>> Sent from my Verizon Wireless BlackBerry
>>
>> -----Original Message-----
>> From: "George Church" <[email protected]>
>>
>> Date: Sun, 1 Mar 2009 10:12:12
>> To: <[email protected]>
>> Subject: RE: statistics
>>
>>
>> Nothing fancy, a 1" ball valve; or an ITC-type set up if you want to get
>> fancy and run it out, we don't always.
>>
>> Potter has an auto air release you could also use.
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Ergo
>> Sent: Sunday, March 01, 2009 10:02 AM
>> To: [email protected]
>> Subject: Re: statistics
>>
>> George,
>>
>> You have a way to bleed the air off of the system at the high point? This
>> sounds like a good idea. Cold you explain some more on how to make this
>> happen?
>>
>> Thanks,
>>
>>
>> Ergo
>>
>>
>>
>> On Fri, Feb 27, 2009 at 8:38 AM, George Church <[email protected]> wrote:
>>
>>> Venus and Mars. I raise hypothetical questions, you hunter-gatherers
>> answer
>>> the question instead of pursuing the issue of statistics :) and how to
>> find
>>> them. Quite a change from the suggester of a group hug:)
>>>
>>> I agree on the BFP, MIC, and although we often have the ITC on a riser
>>> manifold, we generally have a way to bleed the air off the high point to
>>> avoid false signals.
>>>
>>> Good point on calculating the Expected Value, taking the frequency a step
>>> further and including impact.
>>>
>>> glc
>>>
>>> -----Original Message-----
>>> From: [email protected]
>>> [mailto:[email protected]] On Behalf Of Chris
>>> Cahill
>>> Sent: Friday, February 27, 2009 11:02 AM
>>> To: [email protected]
>>>  Subject: RE: statistics
>>>
>>> But if you are doing a risk analysis you are forgetting the outcome side.
>>> For example, failure of a BFP to protect the public in theory could be
>>> catastrophic to many if not all on the water supply.  Failure of a BFP in
>> a
>>> fire should only affect one building. On the theoretical side some may
> die
>>> from the fire and/or billions of $ lost but it ain't getting a whole city
>>> sick or contaminating an aquifer used by 10's of millions.  So the rates
>>> alone are irrelevant.  You need to take risk and multiply it by loss then
>>> you have the answer on which way to go.  Don't get me wrong BFP's are a
>>> bunch of hooey.
>>>
>>> 1st question - about 0 for both, BFP's are a waste of money in the first
>>> place.
>>>
>>> 2nd - MIC is an issue we need to or will be dealing with more often.
>>> Remember ESF only seems at this point to be an Allied problem. I vote
>> treat
>>> the MIC.
>>>
>>> 3rd - off the end gets some/most air out reducing false alarms and
>>> eliminating some air/water interface rusting.  MIC coatings help with the
>>> added oxygen in the water.  I vote end.
>>>
>>> Chris Cahill, P.E.
>>> Fire Protection Engineer
>>> Sentry Fire Protection, Inc.
>>>
>>> 763-658-4483
>>> 763-658-4921 fax
>>>
>>> Email: [email protected]
>>>
>>> Mail: P.O. Box 69
>>>        Waverly, MN 55390
>>>
>>> Location: 4439 Hwy 12 SW
>>>              Waverly, MN 55390
>>>
>>> -----Original Message-----
>>> From: [email protected]
>>> [mailto:[email protected]] On Behalf Of George
>>> Church
>>> Sent: Friday, February 27, 2009 9:15 AM
>>> To: [email protected]
>>> Subject: statistics
>>>
>>> Just as we recently discussed that we don't know how many heads a year
> are
>>> installed, or how many have been installed in the past 100+ years, when
>>> discussing unexpected activations, statistics of some order of magnitude
>>> would be helpful in numerous other things.
>>>
>>> Which occurs more frequently, failure of a backflow to protect the public
>>> supply, or failure of a backflow to allow full forward flow of water to a
>>> sprinkler system when needed?
>>>
>>> Is the possibility of MIC greater than the likelihood of ESF from MIC
>>> coatings? This would aid us in deciding, on systems comprised of combo
>>> steel
>>> and CPVC, if we want to use uncoated pipe (more susceptible to MIC) or
>> risk
>>> Environmental Stress Fractures?
>>>
>>> Is it better to run the ITC off the riser and limit the new oxygen into
>> the
>>> system, or run it off the tail end and check for blockage?
>>>
>>> There are countless other items we have no data upon which to base our
>>> decisions. Our best guesses may be completely wrong- guess our batting
>>> average would be no better than 50-50, and likely the answer may be based
>>> on
>>> something more important but not considered.
>>>
>>> glc
>>>
>>> -----Original Message-----
>>> From: George Church [mailto:[email protected]]
>>> Sent: Friday, February 27, 2009 10:07 AM
>>> To: '[email protected]'
>>> Subject: RE: Fire marshall
>>>
>>> Just as a plumber would assume testing a sprinkler backflow is limited to
>>> the backflow portion of the test, not aware of the forward flush we're
>> more
>>> concerned about.
>>>
>>> glc
>>>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
>
> This document should only be read by those persons to whom it is addressed 
> and is not intended to be relied upon by any person without subsequent 
> written confirmation of its contents. Accordingly, our company disclaim all 
> responsibility and accept no liability (including in negligence) for the 
> consequences for any person acting, or refraining from acting, on such 
> information prior to the receipt by those persons of subsequent written 
> confirmation.
>
> If you have received this e-mail message in error, please notify us 
> immediately by telephone. Please also destroy and delete the message from 
> your computer. The Unsolicited Electronic Message Act 2007 (The Spam Act) 
> came into effect from 5 September 2007. As a valued client you may receive 
> communications from us from time to time, including electronic publications, 
> invitations and related information. Please advise if you wish us to stop 
> sending these communications to you. Otherwise we will assume you wish to 
> continue receiving these communications from us.
>
> Any form of reproduction, dissemination, copying, disclosure, modification, 
> distribution and/or publication of this e-mail message is strictly prohibited.
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
at home....