Here here. We witness the very same problem on large wet gridded systems, just as your experience and research indicates.

We have one AHJ would REQUIRES test/drain ITCs. Guess where my false alarming issues are? I suspect this AHJ requirement is for their convenience and is not based on scientific laws of hydraulics and certainly not based on NFPA recommendations or typical trade practice. We have to live with the unintended consequences as a result of this "design compromise/requirement".

Byron

Byron Blake, CET
Service/Inspections
Freedom Fire Protection, LLC
Longmont, CO

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Rodney Hamm
Sent: Sunday, March 01, 2009 5:38 PM
To: [email protected]
Subject: RE: statistics

If anyone has any pull or influence with the development of NFPA 13........

Please discuss the idiotic approach of installing Inspector's Test Connections at the sprinkler riser (~12 in. downstream of the flow switch). This has been considered "acceptable" by NFPA 13 since 2002 and is quickly becoming standard practice in the great state of Georgia. There are several significant reasons why this is a bad idea AND from an engineering standpoint this is a very poor design. The inevitable trapped air in the system causes or can potentially cause a number of problems: Excessive system pressure when temperatures increase, false water flow alarms due to air pocket expansion/contraction, failed water flow alarms due to cycling flow switches, increased rust on the interior surfaces of sprinkler piping, etc.

From what I have seen, most contractors or sprinkler designers who
primarily
install or design new systems have no idea this approach causes problems for the building owner and/or fire protection system inspectors. I can confirm these are common problems at several of the facilities I have visited over the past few years. In many instances, the only effective solution is to install a suitably located Inspector's Test Connection or bleed the air pockets using sprinklers at the highest elevations. We have installed air bleed off connections for numerous systems simply to allow trapped air to be removed from the high point. The problem is access at some facilities after the solid ceilings or other obstructions have been introduced.

In my humble opinion, Inspector's Test Connections should be installed at the most remote point of each system. The connection point (prior to being piped to within 6 ft. of the floor level) should be at the highest elevation of the sprinkler system piping whenever possible. Auxiliary drains or low point drains should NOT be considered Inspector's Test Connections.

I would assume it is safe to say anyone who has enough experience and personal dealings with inspections and/or problem solving (after the design phase and initial installation project has been completed) realizes that the Inspector's Test Connection serves more purposes than just testing the water flow alarms. {I have heard "the sole purpose of the ITC is to test the alarm device" so many times that I get a smile every time someone spouts it.} I simply disagree with the relatively recent change in NFPA 13 which allows this approach. I strongly believe the practice of installing the Inspector's Test Connection a few feet downstream of the water flow switch should be considered unacceptable.

In many instances, the fire alarm companies and building owners have to deal with the issues caused by this poor design. They rarely if ever realize the true source or reason for the intermittent false alarms. They simple bypass the alarm or set the delays so high that flow switch cycling becomes a problem during alarm testing.

We see systems with >175 psi on a regular basis caused by this problem.......some systems even peg the 300 psi gauges. On of my customers had 5 separate incidents where sprinklers developed leaks and/or popped open due to excess system pressure during Spring & early Summer of 2007. We added pressure relief valves in August of 2007 for all of their wet systems and this resolved the problem. This is a >1 million sq. ft. facility with several wet systems. False fire alarms and excess air pressure are very common problems when the ITC is not located at the most remote and/or highest elevation of the system piping. I could provide many more examples, but I think I have made my point.

Black steel, moisture and trapped air allows more rust to develop on the interior surfaces of the sprinkler piping than if the majority of the sprinkler piping is full of water. Therefore, it would be safe to conclude that trapped air in the sprinkler systems will shorten the life of the sprinkler system piping.

The fact that someone or some group convinced the NFPA committee to change the standard and the fact that the approach saves time and money during installation does not make it a good engineering design!

There are probably a few instances where placing the ITC a few feet downstream of the flow switch should be considered acceptable due to limited or no feasible alternatives; however, these instances should be the last resort alternative rather than standard practice.

Just one man's perspective!! I wonder if anyone on this forum agrees with me on this subject.

Rodney K. Hamm, P.E.
President/Owner
Falcon Fire Protection
Office  (478) 953-1677
Cell  (478) 396-6988


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to