Short answer is yes an AHJ can require buildings to be brought up to modern standards. There are 3 ways to do this I can think of.
First, was it correct 20 years ago? If not they can clearly enforce. Now the legal assumption usually is it was correct and the AHJ needs to show it wasn't. I'm thinking you are describing PODS. There's an argument as I interpret what you described it isn't in today's code how to do it correctly so it surely wasn't there 20 years ago. Even if not PODS it's still a question. Second, if it was correct could use the distinct hazard test. Basically saying it was OK at a time but in 20 years we have learned more about the issue and what was OK 20 years ago is not today. Again AHJ needs to make the case of what constitutes a distinct hazard. If the owner appeals this might be a tough sell to the judge so one doesn't use this willy-nilly. And he better be doing the analysis on every building of a similar class. Third, did it change use or hazard over the years? HPS may not change occupancy class but if there are say more plastics today than originally stored could use this twist. In theory this can even be used in an example of 18' plastics then but no sprinklers and now 16' metal widgets but with the changes of standards would require sprinklers. Lesser hazard now requires more protection. Check IFC 102. But as Todd said check the local codes too. Perhaps the adopting authority modified this section. IBC wouldn't have any real bearing as it's existing. THERE IS NO SUCH THING AS A GRANDFATHER CLAUSE! But it's also not easy on the AHJ to get existing things brought up to modern codes. If it was correct then and hasn't changed use and you can prove it the distinct hazard is all that's left making it real close to a grandfather clause but a sharp AHJ can work this. Chris Cahill, P.E. Fire Protection Engineer Sentry Fire Protection, Inc. 763-658-4483 763-658-4921 fax Email: [email protected] Mail: P.O. Box 69 Waverly, MN 55390 Location: 4439 Hwy 12 SW Waverly, MN 55390 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Ford, Charles Sent: Tuesday, March 10, 2009 11:07 AM To: [email protected] Subject: RE: high rack storage I have been asked if a local AHJ can enforce high rack storage sprinklers (or the equivalent) in a moving and storage warehouse. Boxed and unboxed household goods . Building has only ceiling sprinklers. Same occupancy for 20+ years. State code is IBC -2006 and local IFC 2006. I would think that this has pretty well established but I guess not. Can it vary depending on State or locality? C. Burton Ford Designer- NICET Certified: Fire Alarm, Special Hazards, Sprinkler Design &Sprinkler Inspections NFPA CFPS Cintas Fire Protection-D-47 Warminster, PA 18974 Phone 267-487-1000 Fax 267-487-1010 This e-mail transmission contains information that is intended to be confidential and privileged. If you receive this e-mail and you are not a named addressee you are hereby notified that you are not authorized to read, print, retain, copy or disseminate this communication without the consent of the sender and that doing so is prohibited and may be unlawful. Please reply to the message immediately by informing the sender that the message was misdirected. After replying, please delete and otherwise erase it and any attachments from your computer system. Your assistance in correcting this error is appreciated. _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)