Short answer is yes an AHJ can require buildings to be brought up to modern
standards.  There are 3 ways to do this I can think of.  

First, was it correct 20 years ago?  If not they can clearly enforce.  Now
the legal assumption usually is it was correct and the AHJ needs to show it
wasn't. I'm thinking you are describing PODS. There's an argument as I
interpret what you described it isn't in today's code how to do it correctly
so it surely wasn't there 20 years ago.  Even if not PODS it's still a
question. 

Second, if it was correct could use the distinct hazard test.  Basically
saying it was OK at a time but in 20 years we have learned more about the
issue and what was OK 20 years ago is not today.  Again AHJ needs to make
the case of what constitutes a distinct hazard.  If the owner appeals this
might be a tough sell to the judge so one doesn't use this willy-nilly.  And
he better be doing the analysis on every building of a similar class.  

Third, did it change use or hazard over the years?  HPS may not change
occupancy class but if there are say more plastics today than originally
stored could use this twist.  In theory this can even be used in an example
of 18' plastics then but no sprinklers and now 16' metal widgets but with
the changes of standards would require sprinklers.  Lesser hazard now
requires more protection.      

Check IFC 102.  But as Todd said check the local codes too. Perhaps the
adopting authority modified this section.  IBC wouldn't have any real
bearing as it's existing. 

THERE IS NO SUCH THING AS A GRANDFATHER CLAUSE!  But it's also not easy on
the AHJ to get existing things brought up to modern codes.  If it was
correct then and hasn't changed use and you can prove it the distinct hazard
is all that's left making it real close to a grandfather clause but a sharp
AHJ can work this.  

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ford, Charles
Sent: Tuesday, March 10, 2009 11:07 AM
To: [email protected]
Subject: RE: high rack storage

I have been asked if a local AHJ can enforce high rack storage sprinklers
(or the equivalent) in a
moving and storage warehouse. Boxed and unboxed household goods . Building
has only ceiling
sprinklers. Same occupancy for 20+ years. State code is IBC -2006 and local
IFC 2006. 

 I would think that this has pretty well established but I guess not. Can it
vary depending on State
or locality?

C. Burton Ford
Designer- NICET Certified: Fire Alarm, 
Special Hazards, Sprinkler Design 
&Sprinkler Inspections
NFPA CFPS
Cintas Fire Protection-D-47
Warminster, PA 18974
Phone 267-487-1000
Fax 267-487-1010



This e-mail transmission contains information that is intended to be
confidential and privileged.  If you receive this e-mail and you are not a
named addressee you are hereby notified that you are not authorized to read,
print, retain, copy or disseminate this communication without the consent of
the sender and that doing so is prohibited and may be unlawful.  Please
reply to the message immediately by informing the sender that the message
was misdirected.  After replying, please delete and otherwise erase it and
any attachments from your computer system.  Your assistance in correcting
this error is appreciated.
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to