Only in buildings classified as high-rise, if I'm not mistaken.  

 
Sent from my Verizon Wireless BlackBerry

-----Original Message-----
From: "Tom Duross" <[email protected]>

Date: Thu, 26 Mar 2009 05:31:55 
To: <[email protected]>
Subject: RE: side by side standpipes


I don't see many scissor stairs here in MA much anymore but I always thought 
smoke vestibules were required with scissor stairs? 
Tom 
 
George wrote; "It drops us outside the hotel in a fenced enclosure where we 
can't get more than 10' from the building." 
2006 IBC/NJ 1024.6 Access to a public way. 
The exit discharge shall provide a direct and unobstructed access to a 
public way. 
Exception: Where access to a public way cannot be provided, a safe dispersal 
area shall be provided where all of the following are met: 
1.      The area shall be of a size to accommodate at least 5 square feet 
(0.28 m2) for each person. 
2.      The area shall be located on the same lot at least 50 feet (15 240 
mm) away from the building requiring egress. 
3.      The area shall be permanently maintained and identified as a safe 
dispersal area. 
4.      The area shall be provided with a safe and unobstructed path of 
travel from the building. 
Name the town (off list of course) and I'll send you the name of the fire 
marshal, building and fire subcode officials.  Or if you so choose I'll send 
this to them myself. 
John Drucker 
Fire Protection Subcode Official 
Building/Fire/Electrical Inspector 
New Jersey 
PS, Steve and Terry, good idea avoid the main exit, use a secondary exit 
(remember what the flight attendant always tells you) However find comfort 
that NJ has increased the main exit capacity requirements from 50% to 66.66% 
of total occupant load for A-2 nightclubs amongst other fire safety 
requirements.  As for overcrowds, blocked exits and the like a call to the 
FM's usually results in evacuation of the premises and closure where 
necessary. In our jurisdiction the owners are well aware of this and take 
the time to police there establishments knowing well the cost of not doing 
so. 
PSS, Partially agree on Hose Valves in stairways. Cook County is a prime 
example, deployment of the hose line onto the fire floor means a breached 
opening protective, i.e. the stairway door is ajar by the hose line. What's 
the solution ?  Hose valves on the fire floor ?, that means we have to open 
the door, go onto the floor and attempt to setup and hookup without the 
protection of a charged line. 
The solution may be protected smoke tight corridors between the stair and 
the floor, think of it like an airlock. The hose valve is located in the 
corridor. Firefighters come up the stair, into the corridor, make their 
connection on the fire floor and deploy. The corridor allows them enough 
space to stretch out the charged hoseline. The stairways integrity is 
maintained. 
 
John Drucker 
I'd have paid for you and T's tix to witness that dialogue! 
Well, in a previous economy I would have.... 
We were up in N jersey for an annual FA guy's bash for customers and AHJs. 4 
AM the FA goes off in the hotel, we exit at measured pace (spkrs in hotel, 
but not QR) thru nearest stair (required one, I'm sure). It drops us outside 
the hotel in a fenced enclosure where we can't get more than 10' from the 
building. Now I point out that we're only looking at a blank masonry wall 
facing us, so there's limited exposure to a fire in the building, and I know 
I can throw her over the fence and get over it myself if we had to- but we 
go back in to the lobby with the other assembled guests (quite a fashion 
show) and await the FD's arrival when we'll be kicked out into the cold 
while the FD does a walk thru to confirm no fire, FD arrives and the 
incident commander no sooner is in the building a minute before red is in 
his face griping about our being trapped outside. I'm sure this is just what 
thihs guy wants when responding to a nuisance alarm at 4 AM a week or two 
before Christmas....but believe me, the point was made. 
glc 
_______________________________________________ 
Sprinklerforum mailing list 
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
<http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum> 
For Technical Assistance, send an email to: [email protected] 
To Unsubscribe, send an email to:[email protected] 
(Put the word unsubscribe in the subject field) 
  
__________ Information from ESET NOD32 Antivirus, version of virus signature 
database 3965 (20090326)__________ 
The message was checked by ESET NOD32 Antivirus. 
http://www.eset.com <http://www.eset.com> 
  
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to